Having a continuous burn problem with my gas furnace. In a cycle, the following happens:
1) Hear the relays click in the furnace.
2) In about 20 seconds the 3 gas jets ignite and burn for about 30 seconds
3) At this time the blower kicks on, and the jets turn off immediately.
4) For the next 1.5 minutes the blower keeps going, and during this time
the igniters turn on and glow for about 2 more times - but no gas.
5) Finally, the blower steps up its speed considerably before shutting off.
6) The furnace then won't come back on for about 20 minutes, unless the
power is turned off and back on, or the digital thermostat is turned down
then back up.
What's also interesting is that the control board on the furnace is in default
configuration which is 2 stage, yet the thermostat is wired for single stage.

I've measured the voltage potential between the red & green, and the
red & white. When the furnace starts the voltage drops to zero
between the red & white as I'd expect, but is otherwise at about 25v.
On the other hand, the voltage between the red & green is constantly
at 25v regardless of what is going on.

Any help wouid be appreciated.
 