Installing 220v circuit
Discussion in 'Electrical Forum discussion & Blog' started by Keith Wolf Ent, Jun 14, 2008.
  1. Keith Wolf Ent
    Keith Wolf Ent New Member
    Jun 13, 2008
    Hey, I am adding an A/C compressor for central air , need to run 220 for about 75 feet outdoors. Has to be to code - Any ideas on any/all of the following?
    1) Can I use plastic conduit or must it be metal? How about flexible metal wrapped (and then NOT enclosed)?
    2) Is a 2P 20 Amp 3-wire breaker actually a 40 Amp breaker?
    3) Is 10/3 600v the right wire?
    4) Need a shutoff box at the compressor unit - any recommendations?
    The compressor is a Goodman GSC-14 SEER, the coil is already in the central furnace.
    Thanks,
    Keith
  2. jimbo
    jimbo Plumber
    You need help.
    2) NO. 20 amps is 20 amps. If the circuit is 240 volts, as opposed to 120, the breaker is 2 poles ( 2 switches) but 20 is 20......and that would not be big enough for most AC.
    3) You have to get an electrician to look at the specs and the install manual for your air conditioner, determine what circuit breaker size is required, and the NEC will tell him what size wire to use, based on the amps and the distance.
    A fused, or non-fused, disconnect, is a very common and necessary item for an AC install. Even HD would have one. Keep in mind that your local building code may require you to install a 120 volt service outlet adjacent to the outside unit.
    How old is the inside coil? When is was installed, was it known that the outside unit would be 13/14 SEER? If not, you CANNOT use it. Also, the GSC 14 is available in R-22 and R-410 versions. Which is yours? Is the indoor coil rated for the refrigerant system you will be using?
  4. Bob NH
    Bob NH In the Trades
    Oct 20, 2005
    New Hampshire
    You need to look at the installation instructions and the nameplate to determine the wiring and circuit breaker requirement.
    The nameplate of the equipment or compressor should be marked with either a "Rated Load Current" or a "Branch Circuit Selection Current". If it is marked with a Branch Circuit Selection Current; that is used to select conductors and circuit breaker or fuses. If there is no marking for Branch Circuit Selection Current then the Rated Load Current should be used. See NEC Article 440.
    You can't use NM (Romex) outside. THHN/THWN in PVC conduit is a good choice. You should be able to get it all in 3/4" conduit.
    If you need to install a 120 Volt circuit for service you can probably run it in the same conduit. You will have to check the derating due to extra wires in the conduit but it should not be a problem. Derating is from the 90C rating so sizes up to #10 are not affected at all and #8 is derated to 44 Amps.
    You can use a flex conduit at the end but not for the whole run.
  5. Speedy Petey
    Speedy Petey Licensed Electrical Contractor
    Jun 16, 2007
    NY State, USA
    Absolutely. Have an electrician do this job.
  6. Keith Wolf Ent
    Jun 13, 2008
    Thanks for advice...
    The coil is R-22, the unit is 30A max. There are multiple service outlets already at the coil - the (refrigerant/return) lines only have to run 10 feet or so. Caught a rattler up there today, after he almost got me mum! :confused:
  7. jimbo
    jimbo Plumber
    On case coils and air handlers, you can decode the model number to determine the refrigerant. A final digit 6 incates dual compatible~410 & 22. The "C" in the model GSC.....indicates an R-22 unit, so you are good to go on that score.
  8. Speedy Petey
    Jun 16, 2007
    NY State, USA
    How many amps will R-22 carry? :p
  9. jimbo
    jimbo Plumber
    :)R-22 is not measured in amps....it is measured in cubic dollars!!:)
  10. Speedy Petey
    Jun 16, 2007
    NY State, USA
    Wow, look. Another gold spammer who rated his spam with 5 stars.
Similar Threads: Installing 220v
Electrical Forum discussion & Blog Installing an AFCI breaker Jan 5, 2017
Electrical Forum discussion & Blog Homeowner installing electric to hot tub Nov 30, 2014
Electrical Forum discussion & Blog Installing Garbage Disposer electrical Jun 18, 2014
Electrical Forum discussion & Blog What to do with wires when installing light switches/plugs Sep 9, 2013
Electrical Forum discussion & Blog Grease on new Siemens circ. breaker contacts - need to wipe out before installing? Aug 13, 2013