    We hired someone to add outlets in the front yard. This is a new circuit with a GFI on the house leading to 2 boxes in the yard. When the GFI tripped (a fixture got wet), I reset it and nothing worked. I got out my handy tester and it showed hot and ground reversed. I looked in the boxes (with the breaker turned off of course) and saw nothing obviously wired incorrectly. When the power was turned back on and the GFI reset, everything worked. Since then, if the GFI trips, I need to reset it twice to get the line working again.

    What could cause this? I'm already looking at why it trips, but I'd like to know what would cause it to need to be reset a couple times.

    Thanks in advance.
  2. jimbo

    jimbo Plumber

    Messages:
    8,997
    Location:
    San Diego
    A "loophole" in many of the little plug-in outlet testers is that they report and OPEN NEUTRAL as hot/ground reversed. Look for a loose connection on a neutral wire somewhere.
  3. Jeff1

    Jeff1 New Member

    Messages:
    102
    Location:
    So Cal
    Thanks. I'll look into it.
  4. Thatguy

    Thatguy Homeowner

    Messages:
    1,460
    Location:
    MD
    It will soon fail.

    BTW, if you run a 120v test lamp from the GFI short slot to a known good ground it should trip.
Similar Threads: weird issue
Forum Title Date
Electrical Forum discussion & Blog Weird lights blinking, AC compressors making weird noise when it does it. Sep 8, 2013
Electrical Forum discussion & Blog weird wiring and wierd voltages on 3 dual switches... Dec 17, 2012
Electrical Forum discussion & Blog Weird phone line problem... Nov 6, 2011
Electrical Forum discussion & Blog Weird Switch wiring Aug 13, 2007
Electrical Forum discussion & Blog Ceiling Fan Issue - Humming Sound When Light Off May 20, 2014

Share This Page