Furnace not lighting
Discussion in 'HVAC Heating & Cooling' started by Moleculad, Nov 17, 2008.
  1. Moleculad
    Moleculad New Member
    Nov 17, 2008
    My furnace stop lighting some time last week and the temperature is about to drop below freezing. When I open the furnace panel the White Roger ignition switch trouble LED was flashing red, and I could not manually ignite the flame. Is there a way to troubleshoot the switch & the ignition source? I noticed the values for the fuel gas line was wired to the switch and was told there was a 18 seconds period where I could manually lite the flame before a lock out after resetting the furnace.
  2. jadnashua
    First thing I'd do is turn the power to the furnace off for 30-seconds or so, then turn it back on and see if it clears the error.
    Every one is a little different. A typical sequence is: call for heat, apply power to the igniter (if a coil), turn on gas, check for flame, if no flame, shut off gas, run a purge cycle, try again. It will often do this several times until it quits and says there is an error.
    The manual should show the 'normal' operation.
    If it has a sparker, you should hear the clicks when trying to light the gas. If it is a heating coil, you won't hear anything, but there will be a longer delay between call for heat and gas coming on. Sometimes the coil has a dual purpose: ignite the gas and then detect the flame. If it has a sparker, there's a separate flame sensor.
    Any bad component can cause it to not light.
    Could be a bad gas valve, or a plugged gas valve, or a shut off supply. Lots of things. Often the interlocks are fairly easy to diagnose, but you need to be able to read and understand the manual.
    If this is a closed combustion system, a cracked intake pipe will also prevent it from coming on. This is often checked with a vacuum switch interlock.
    If the controller has other lights, the 'normal' sequence would be described. You'd want to watch what's happening with them, and it might lead you to understand what function is not working.
Similar Threads: Furnace lighting
HVAC Heating & Cooling Rheem furnace model r92pa not lighting all the time Jan 24, 2017
HVAC Heating & Cooling Ducane furnace not lighting. Draft inducer or pressure switch? Oct 4, 2010
HVAC Heating & Cooling Ducane furnace still not lighting. No power where ignitor connects to smart valve. Oct 4, 2010
HVAC Heating & Cooling Chattering Furnace Contactor Jan 7, 2017
HVAC Heating & Cooling Dripping Sound from Attic Furnace/AC? Jan 1, 2017