Furnace drain problem

Discussion in 'HVAC Heating & Cooling' started by dsruss, Dec 1, 2008.

  1. dsruss

    dsruss New Member

    Joined:
    Dec 1, 2008
    Hello,

    I have a problem with the condensation drain of my furnace. The problem is that it currently drains into a bucket I have to empty regularly. The guy who owned/built the house before me finished the basement and used the one floor drain for the shower and so now the furnace does not have a way to drain to it. I opened up the sheetrock a bit on the wall next to the furnace and found that there is a 1 1/2 inch vent pipe in the wall going down into the slab. Would it be okay to put a little "Y" on this pipe and let my furnace drain into it? Is this a good solution? If it is possible for me to run a flexible hose up through the wall and down into the shower, would a condensate pump be a better fix?
     
  2. jadnashua

    jadnashua Retired Defense Industry Engineer xxx

    Joined:
    Sep 2, 2004
    Occupation:
    Retired Systems engineer for defense industry.
    Location:
    New England
    A vent used as a drain is no longer a vent! If you did find a place where you could put it, it would need a trap to keep sewer gasses from escaping. You'd want to ensure the trap didn't dry out when you weren't using the furnace, or it would dry out and start to smell.

    I'd consider a condensate pump. Now, where to dump it becomes an issue. A condensate pump can be purchased with various head capabilities, so you could pump it up a ways, maybe into a dishwasher type connection into an existing drain - maybe in the kitchen. Not sure about the code requirements.
     
  3. Sponsor

    Sponsor Paid Advertisement

     
  4. burleymike

    burleymike New Member

    Joined:
    Nov 4, 2008
    Location:
    Idaho
    I would go with a condensate pump. Depending on were you live you may be able to have it drain outside, check with your local building official.
     
  5. veesubotee

    veesubotee New Member

    Joined:
    Nov 3, 2008
    By all means, use a pump.

    I just had my system replaced with a 95% furnace and a/c. The condensate is pumped up about 15 feet and discharged into a first floor laundry tub. (my design)

    Now I can monitor the operation of my furnace-a/c conveniently. No freeze-ups in the winter.

    V
     
Similar Threads: Furnace drain
Forum Title Date
HVAC Heating & Cooling Condensating furnace drain line problem Sep 13, 2013
HVAC Heating & Cooling New furnace draining into foundation -- overflow Dec 9, 2012
HVAC Heating & Cooling Replacing furnace - wondering about flex duct sizing Jun 14, 2015
HVAC Heating & Cooling Furnace Starts up Choppy Feb 20, 2015
HVAC Heating & Cooling 7 red flashes - York furnace Feb 17, 2015

Share This Page