What kind of a T do I use when connecting, in the attic, above any waterline, a sink vent into a second horizontal sink vent.
The main stack has a 90 degree 1 1/2 pipe stub just below the roof where the main stack exits. Both sink vents are running horizontal and joined together in a T just before entering the stub to the main stack. The iron pipe has all rotted and I assumed that I could replace with a simple 1 1/2 x 1 1/2 x 1 1/2 T. I presume I should not use a sanitary T or a Wye.

Is that correct?
 

wwhitney

In the Trades
Messages
6,567
Reaction score
1,847
Points
113
Location
Berkeley, CA
For dry vent 6" above any fixture flood rim, you can use basically any fitting you want. Sanitary tee would be fine and might be easier to find or cheaper than a vent tee.

Cheers, Wayne
 

wwhitney

In the Trades
Messages
6,567
Reaction score
1,847
Points
113
Location
Berkeley, CA
When used for connecting vents only, it is conventional, but I believe not required, that a sanitary tee with the barrel vertical is flipped upside.

Cheers, Wayne
 

Barry

New Member
Messages
13
Reaction score
0
Points
1
Location
Minnesota
OK. So either a standard Vent T if I can find one or a sanitary T (in this case laying horizontal) with the normally downside (when vertical) facing toward the main stack.
 