Connecting a 4" cast iron pipe cut flush with concrete

Users who are viewing this thread

Marzec

New Member
Messages
23
Reaction score
2
Points
3
Location
Ohio
I am rehabbing one of my apartments that sits above a garage and I have a situation where the a 4" cast iron soil stack in a garage has been cut flush with the concrete floor. The stack was already broken at garage floor level and therefore needed to be replaced. Unfortunately, since it was broken at floor level there was no way to leave even an inch or two of it above the floor for a shielded rubber coupler. I am familiar with the rubber bushings that fit into a cast iron hub to make an easy transition to PVC, but I am unaware of anything available that is made to fit directly into a 4" cast iron pipe to make this transition.

My question is, is there is anything that exists for this situation to transition to 3" PVC or is the best practice to bust out enough concrete to use rubber coupler that can at least be partially buried? I don't have a photo of it at the moment, but basically just imagine a 4" cast iron pipe cut flush with a concrete floor.

I read about a similar situation on this forum where someone suggested the possibility of using a closet flange with the rubber gasket made to go into 4" pipe, but that sounds hacky and not something that will hold up over time. I think the person ended up digging it out anyway.
 

Jeff H Young

In the Trades
Messages
8,962
Reaction score
2,236
Points
113
Location
92346
chip down into slab a few inches put a mission cp 44 band short piece of plastic pipe then glue a 4 inch clean out on then glue a 4x3 bushing in the top of the clean out connect to your 3 inch . Id put the clean out in but you can skip that step I wouldnt though
 

Marzec

New Member
Messages
23
Reaction score
2
Points
3
Location
Ohio
chip down into slab a few inches put a mission cp 44 band short piece of plastic pipe then glue a 4 inch clean out on then glue a 4x3 bushing in the top of the clean out connect to your 3 inch . Id put the clean out in but you can skip that step I wouldnt though
Sounds like great advice. Thanks!

Not sure if the plumbing supply house I go to carries Mission, but I assume any quality shielded stainless steel band for CI to PVC should work. And yeah, I will install a cleanout.
 

Jeff H Young

In the Trades
Messages
8,962
Reaction score
2,236
Points
113
Location
92346
other brands are fine like fernco , Sounds like you are aware of the proper type band.
I would be careful chipping out concrete not to damage the cast iron maybe drill holes a few inches away first varound the pipe
 
Top