Conduit Runs and box wireing
Discussion in 'Electrical Forum discussion & Blog' started by Giles, Feb 19, 2011.
  1. Giles
    Giles Retired tool & Die and Mechanic
    Aug 28, 2007
    Retired
    N.W. Alabama--Florence--
    I am adding a branch circuit box to a storage room. This box will supply power for a 220v welder and a small 220 4K watt heater. I have noticed that all the 110v wireing is in 1/2" conduit from the celing down.
    Is this required by most codes, and what about "overhead runs"?
    Also, since this box will be mounted in a joining separate room with main breaker panel, what are the grounding rules--since there is no main breaker and no way to bond the ground on the new box?
  2. cacher_chick
    Jan 5, 2008
    Test, Don't Guess!
    Wiring must be in conduit where in places where it must be protected from physical harm. Some local codes require conduit throughout.
    I don't understand your question regarding grounding.
    All metal electrical boxes and receptacles must be grounded, be it through conduit and/or a separate ground wire.
  4. Giles
    Aug 28, 2007
    Retired
    The box I am installing does not have a main disconnect. It is a QO square D, 6 space #QO6-12L100S. It is my understanding that a sub panel must be bonded and I know how this is done. However there is no way to disconnect the grounds and neutrals as there is only one ground bar. There is a bonding screw.
    I plan to run supply wires from the main panel just as I would if I were adding a 220v recepticle.
    Is this correct?
    I am not new to electrical work but I am not an electrician. I go to the extremes sometimes to make sure it is done correct, and I think that is good.
    THANKS for helping.
  5. drick
    drick In the Trades
    May 16, 2008
    You need a separate ground bar. You can purchase these separately. Just screw one into the back box. There are usually unused screw holes in the back of the box for this purpose and the bar usually includes the screws. The existing bar should be isolated from the box. This is your neutral bar. Just remove the grounding screw from it. Unlike in your main panel neutrals and grounds must be kept separate in a sub panel.
    -rick
  6. LLigetfa
    Feb 6, 2011
    Information Technology
    NW Ontario, Canada
    In our regulatory domain, I don't believe that metal conduit is adequate for grounding and that a ground wire is required.
  7. jwelectric
    jwelectric Electrical Contractor/Instructor
    Jun 14, 2007
    Instructor
    North Carolina
    250.118 Types of Equipment Grounding Conductors.
    The equipment grounding conductor run with or enclosing
    the circuit conductors shall be one or more or a combination
    of the following:
    FPN: For effective ground-fault current path, see 250.2
    Definition.
    (1) A copper, aluminum, or copper-clad aluminum conductor.
    This conductor shall be solid or stranded; insulated,
    covered, or bare; and in the form of a wire or
    a busbar of any shape.
    (2) Rigid metal conduit.
    (3) Intermediate metal conduit.
    (4) Electrical metallic tubing.
Similar Threads: Conduit Runs
Electrical Forum discussion & Blog Conduit Underground from House to Garage (+water) Sep 29, 2016
Electrical Forum discussion & Blog Conduit Entering Elevated Steel SIP Home Aug 24, 2016
Electrical Forum discussion & Blog Cat5/Coax run short distance along side electric conduit Jul 18, 2016
Electrical Forum discussion & Blog NM buried in plastic conduit Jun 28, 2016
Electrical Forum discussion & Blog How many #6 wires in 3/4 inch rigid conduit? Jun 8, 2016