Can you have bend between vent and washing machine standpipe.

Users who are viewing this thread

fatfingers

New Member
Messages
4
Reaction score
0
Points
1
Location
oregon
I need to move the standpipe 3.5 inches furty from a basement wall.

First thought was rotating the p-trap but have concerns about flow.

Other option is to add two 45's between the vent and the standpipe. Not sure if this is a good idea or if it's a lot by code.

You see any issues with this? All comments greatly appreciated as I spent way too much time thinking and googling about this.
 

wwhitney

In the Trades
Messages
6,567
Reaction score
1,847
Points
113
Location
Berkeley, CA
Turning the trap outlet elbow/u-bend is the first choice, there's no upside to the assembly being "flat". Then add one horizontal 45 if required for further offset.

Cheers, Wayne
 