I need a LWCO with manual reset and a high limit with manual rest. The 3200 would make this boiler more efficient also. There are some wires that go to limit switches from the transformer that I do not know where they should go. DIY home owner.
Don't think much of the control.
Keeps pump or pumps off till water temp gets to 140° cast boilers don't like to be shocked by cold water in the system they like a gradual start
Manual high limit your boiler has a limit.
Low water cut off want a sensor in the water not in a well. Can be electronic or float type.
Outdoor reset there are lots of brands that sell them.
Minimum return water temp 140° for cast boilers. Like warm boilers.