Can I move an existing AAV?

Discussion in 'Plumbing Forum, Professional & DIY Advice, Tips & ' started by n00bie, Dec 8, 2007.

  1. n00bie

    n00bie New Member

    Messages:
    1
    Location:
    Florida
    I was searching around and ran into a similar thread here, but it didn't answer my questions. Sorry for the new posting.

    What I'm doing is nothing more than installing a new sink. However, this new sink has real deep bowls (10" on one side, 8" on the other as opposed to the current 6" double-bowl). If I install the sink right now, it will hit my AAV preventing the sink to seat.

    I need to move my vent and I plan on re-piping to turn that 45, attached below the current vent, to the right, go across about 5", then up to just below my 8" bowl using a studor mini vent. And if that doesn't work, just moving it somewhere to satisfy the manufacturer's instructions. I have a picture of what's going on under and behind the sink. This house was built by a builder in '00 and hasn't been modified since.

    My questions:
    1) It seems my only limitations are "4 inches above the trap's weir" and "below the flood fill line of the fixture". Can I just reroute the vent to anywhere that works for me based on those rules?
    2) When I cut away the existing PVC for the vent, is it going to smell really bad? Do I need to have a plan in place to move fast?
    3) If it helps, my current aav is a Durgo BA5094

    Thanks for any info or existing links. I'm hoping this will be a simple operation - and I think it will be, just want to make sure.

    Attached Files:

    • p1.jpg
      p1.jpg
      File size:
      32.6 KB
      Views:
      139
    • p2.jpg
      p2.jpg
      File size:
      24.8 KB
      Views:
      127
  2. probably so....

    As nasty as that whole configuration looks,

    I cant see how you could possibly hurt it. or

    make it functioin any worse...
  3. Cass

    Cass Plumber

    Messages:
    5,980
    Location:
    Ohio
    Mark is right.

    Each trap should have its own vent B 4 they join together down stream.

    The set up is wrong and the traps will siphon out when either sink is used or the garbage disposal is used.
  4. hj

    hj Moderator & Master Plumber Staff Member

    Messages:
    26,304
    Location:
    Cave Creek, Arizona
    aav

    Where it is currently installed is definitely not "above the floor line of the fixture", but what are the two lines in the second picture and where do they go"
Similar Threads: move existing
Forum Title Date
Plumbing Forum, Professional & DIY Advice, Tips & Inserting a sanitary tee into existing stack that will not move Apr 28, 2013
Plumbing Forum, Professional & DIY Advice, Tips & Move Shutoff Valve to Install Filter Jul 11, 2014
Plumbing Forum, Professional & DIY Advice, Tips & How Do I Remove Accor Plastic Push-Pull Supply Valves? Jun 21, 2014
Plumbing Forum, Professional & DIY Advice, Tips & How do I remove this shower pan/drain in basement? Jun 8, 2014
Plumbing Forum, Professional & DIY Advice, Tips & Can this 1/2" copper line be moved? Jun 4, 2014

Share This Page