bit of confusion now...
solutions
As per a previous thread i started re: re wireing
Actually it should be grounding a un grounded house short of a complete re wire... Anyway what i mean by confusion is this..I have talked to several qualified,licensed,experienced etc. electricians.
1. Some, say all receptacles in the dwelling need GFCI's,
2.some say the first receptacle in each circuit needs a GFCI, wired in so it protects all other receps. downstream in that circuit.A sticker stating "No equipment ground" and visable also needs to be in place all receps.
3. One electrician said it is wortless and a waste to try and acheieve a ground with GFCI's.
I realize GFCI's may not give me a "proper ground" but as long as they make for safer wireing, and protects all equipment plugged into those receptacles and NEC recognizes it as acceptable code compliant etc. I am favoring the idea. Plus i am told the existing three prong outlets now in place can be kept as long as they are protected as mentioned above in 2.
Lakee911
I&C Engineer (mostly WWTP)
Columbus, OH
Number 2 is the safest without a rewire (assuming you don't have metallic conduit). Putting some devices (such as a flourescent light) on a GFCI can lead to nuissence trips, in the case of number 2 it would shut off anything "downstream." My opinion...
Jason
Jdoll42
Computer Systems Engineer
In Illinois near St. Louis, MO
If you wire them in series properly, the first GFCI in the chain will protect anything that follows it.
2.some say the first receptacle in each circuit needs a GFCI, wired in so it protects all other receps. downstream in that circuit. A sticker stating "No equipment ground" and visable also needs to be in place all receps.
Bingo! Your GFCI's should also come with stickers that you can put on the outlets beyond the GFCI to indicate they are also GFCI protected.
I'm not an electrician, but don't GFCI's work off of the ground wire (GROUND fault circuit interrupter)? If none of the outlets have a ground wire, isn't the GFCI pretty much useless?
pudge565
no they dont work with the ground this is a typical misconception. it detects ground faults by measureing the crurrent between the hot and neutral wire a difference of 4-6 miliamps will trip the gfci.
Jdoll42
Ok. I get it now. It detects the current going to ground ELSEWHERE on the circuit instead of back through the neutral wire, thus the Ground Fault part. If the current on the hot wire doesn't match the current on the neutral wire, it's going somewhere it's not supposed to.
Well you learn something new every day. Thanks for the clarification!
Some electronics use the ground wire to help shield or filter noise propagation or reception from interferring with things. A GFCI won't help that if there isn't a real ground, but from a safety viewpoint (i.e., to keep from getting shocked), they work great. Depends on what you are trying to do...a complete rewire is the better way to do things, but you'd probably find you need to add a bunch more outlets and maybe circuits, too and the costs can be quite high. You have to decide what good enough is...
KD
GFCI will trip at 5 mili amps, not 4.
Chris75
Electrician
Litchfield, CT
FWIW, most home appliances are only two wire anyhow, so why not just replace your existing receptacles with two wire receptacles? Then either rewire or install GFCI's where you actually need a 3 wire receptacle.
Alectrician
DIY Senior Member
Use GFCI breakers.
You will save hours of trying to find out what feeds what.
You still have no ground but you eliminate the chance of being hurt by a fault to ground.
Most surge protectors wont work without a ground.
pudge565
i believe that i read the 4-6 mili amp thing in mullins text residential wiring 15th edition not quite sure if it was or not i will check on tuesday wen i go back to tech.
