Bathroom Exhaust Vent. Soffit -vs- Wall.

Discussion in 'HVAC Heating & Cooling' started by bjferri, Jun 7, 2007.

  1. bjferri

    bjferri DoD Army

    Messages:
    150
    Location:
    Maryland
    I have a low profile 80 cfm Panasonic fan w/ an optional 3" vent adapter. Literature states going from 4" to 3" reduces cfm to 70, and increases .5 sones to .6. I'm okay with that...are there disadvantages to going 3� Another thread someone posted stated vibrations. I haven’t installed it yet.

    My main question…my attic floor is open so I can run the vent to either the soffitt or would this cause moisture issues. I should be able to bypass the soffit and run it down the wall cavity and out the house., unless there's a 2x4in the way then I'm stuck. Which is best? I’ve never done this before and making holes in the house gives me a queasy stomach.
  2. jadnashua

    jadnashua Retired Defense Industry Engineer xxx

    Messages:
    22,354
    Location:
    New England
    Running it down a wall cavity isn't very efficient (hot air rises). You might be able to run it out the wall under the sofit by just running down the bottom of the ceiling joist bay. But, so you don't fight the tendency of the hot air to rise, running it out a roof vent works better - probably a shorter run and works good. I'd run the 4" and forget the reducer. Panasonic is a good brand, so it probably wouldn't cause vibrations, but you might end up using a little more electricity, it'll be a little noisier (you may not notice), and it won't move as much air.
  3. bjferri

    bjferri DoD Army

    Messages:
    150
    Location:
    Maryland
    Thanks, but I can't do the roof - if it were a first floor roof okay, but not a second floor pitched roof! Call me chicken. I'll try the wall under the soffit...or can I place the vent close to the attic fan that is nearby and let it out that way...if you think this is good practice? It may look odd. I don't like short cuts just to make things easier so I do want to do this right the first time and asthetics are important.

    Appreciate it!
  4. jadnashua

    jadnashua Retired Defense Industry Engineer xxx

    Messages:
    22,354
    Location:
    New England
    It really should have its own outlet. Remeber, you are exhausting humid air (except for the occasional organic smells!), so you don't really want that in your attic. If it gets below freezing where you are, you could end up with frost on the inside of the roof, joists, etc...not a good situation.
  5. bjferri

    bjferri DoD Army

    Messages:
    150
    Location:
    Maryland
    Thanks again for the great advice! My thoughts exactly...well, except for the frost on the inside of the attic. That's a frightening scenario I never would have thought of!!
    Last edited: Jun 8, 2007
Similar Threads: Bathroom Exhaust
Forum Title Date
HVAC Heating & Cooling How can I vent a bathroom exhaust fan out of the window without it looking hideous? Dec 1, 2010
HVAC Heating & Cooling Inline bathroom exhaust fan sizing Sep 17, 2010
HVAC Heating & Cooling Bathroom Exhaust Fan Oct 27, 2009
HVAC Heating & Cooling Bathroom Exhaust May 7, 2008
HVAC Heating & Cooling Venting multiple bathroom exhaust fans Apr 6, 2008

Share This Page