Bad breaker or ground fault?

Discussion in 'Electrical Forum discussion & Blog' started by cacher_chick, Mar 20, 2013.

  1. bluebinky

    bluebinky Member

    Aug 31, 2011
    Software Engineer
    Santa Clara, CA
    Unhook the neutral and hot (load side) from the GFCI breaker and measure the resistance (VOM and/or megger) between the neutral wire and the neutral bar -- it should be open.

    In my limited experience with residential wiring (I am not a pro in that area), it's not uncommon for neutrals from different circuits to be intentionally tied together (obvious DIY hacks), but in that case, a GFCI breaker *should* always trip with a load on either circuit, and in theory possibly even without any load at all -- depending on the design of breaker.

    I still think what you describe sounds like a flaky breaker. Probably a manufacturing defect...
  2. cacher_chick

    cacher_chick Test, Don't Guess!

    Jan 5, 2008
    Test, Don't Guess!
    Land of Cheese
    As I mentioned before, this was an issue that I resolved some time ago. The reason for my post was to gain insight on how others would go about diagnosing such a problem.

    It was a neutral to ground short, and while my ohmeter showed infinity, the megger did not.

    I started at the panel and spit the circuit in half twice before being confident that it was in the lights. Unfortunately, I had to cut apart all 4 recessed cans to pinpoint the fault. The lights were split wired with 12-3 from 2 switches, and the short was located where the last recessed can junction box NM cable clamp was tightened on the cable.

    After replacing the lights, I loaded the circuit over 20 amps and the GFCI breaker never as much as whimpered.
    Last edited: Mar 22, 2013
  3. jwelectric

    jwelectric Electrical Contractor/Instructor

    Jun 14, 2007
    North Carolina
    You answered your own question. This type problem is never easy to find
Similar Threads: breaker ground
Forum Title Date
Electrical Forum discussion & Blog Can neutral and ground from 50A breaker be shared Apr 21, 2013
Electrical Forum discussion & Blog Neutral/ground at sub breaker panel Aug 16, 2007
Electrical Forum discussion & Blog Quad breaker in 42 space box? Oct 22, 2015
Electrical Forum discussion & Blog Mysterious breaker trip Sep 2, 2015
Electrical Forum discussion & Blog 120v w 19 gallon water heater run on 2 pole 230v breaker. is it safe? Jul 9, 2015

Share This Page