So I am looking to add a wifi Honeywell thermostat to my first zone. Currently it is a simple 2 wire thermostat for a Heat call only. It is a hot water hydronic monoflow loop controlled by a zone valve. Can I simply add a 3rd wire from the 24v transformer to provide the C wire that the thermostat requires?

So use the two existing to control the relay on the zone valve and the new C wire will give the unit the power it needs to do the computer stuff.
 

Stuff

Well-Known Member
Messages
1,221
Reaction score
130
Points
63
Location
Pennsylvania
That is normally how it is done. Make sure to pick the correct wire from the transformer as one of them is already going to your thermostat. So in the end you have R and C coming from the transformer and W going to the zone controller board. Some boards have T and T for the thermostat connections and you have to figure out which one of them is really W.
What zone controller are you using?
 

Rockycmt

Member
Messages
166
Reaction score
1
Points
18
Location
New York Metro Area
So I have 3 zone valves no zone controller. So the transformer powers the 3 valves. I have 2 wires from one zone to the thermostat. Where would the 3rd C wire come from? The transformer directly? If so which wire? the 24v or the neutral?
 

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,771
Reaction score
1,191
Points
113
Location
New England
To make any complete circuit, you need to have a connection from both sides of the secondary on the transformer. All a typical thermostat does is act like a switch that connects the 'hot' (both sides are actually 'hot', but one side might be grounded) to the device in question, and it passes through it, with the other side to the other terminal of the transformer. So, you might need to go back to the transformer, but there may also be a common terminal at the terminal board of the system. In any case, you should be able to measure 24vac between the two leads all of the time - if you can, you've made a complete circuit across the secondary of the transformer.
 

hj

Master Plumber
Messages
33,599
Reaction score
1,037
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
One wire from the transformer goes directly to the controlled device and the other one goes to the thermostat and then to the device. You want your "C" terminal to connect to the side that does NOT go the thermostat.
 