I own one condo unit on the fifth floor of a seven floor building. In the kitchen there is a dishwasher sink and garbage disposal. The drain is very slow and backs up into the dishwasher. Took off garbage disposal and ran a 25 foot snake through as well as using liquid plumber and everything appears to be clean. If I fill the sink with water it bubbles as it drains and goes slow but if I turn on the disposal it drains normally. With my limited knowledge this leads me to believe that there is a vent issue. I don't have access to the vents as they are in the common part of the building.
My question: Can I simply add an AAV or a studor vent right at the fixture, underneath the sink, to help compensate for a potentially blocked vent pipe? If so is there a specific one to use?
 

Tom Sawyer

In the Trades
Messages
3,625
Reaction score
34
Points
48
Location
Maine
Slow drains are NEVER the result of a venting issue unless the fixture drains into a closed container. What you will find is either an obstruction in the drain or a dip or sag in the drain. Most home quality snakes won't do a decent job of clearing a drain either.
 

OffshorePlumber

New Member
Messages
8
Reaction score
1
Points
3
Location
Monroe
Drain is still partially clogged.

It'll drain just fine without a vent, venting systems are designed to maintain trap seals on fixtures.
 

hj

Master Plumber
Messages
33,599
Reaction score
1,037
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
Even if it were a blocked vent, and AAV would be useless in that situation. They allow air in AFTER drainage occurs NOT while, or before, it is draining. "Having" a snake is not the same as using it properly. You are between two other units, so if it were a systemic problem, needing a 25' snake, either the upper one would overflow your sink, or yours would overflow the lower one. AND, because these sinks are interconnected, pipewise, you could NOT have a venting issue.
 

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,771
Reaction score
1,191
Points
113
Location
New England
FWIW, in many places, an air gap is required when installing a dishwasher. This would prevent any backup into the DW. A high loop may or may not meet local code, and doesn't always work, especially if it is not installed properly.

In most places, in a multi-family dwelling, it is illegal to do any plumbing or electrical work without a license...messing something up could create problems for many of your neighbors in the building.
 