DonL
Jack of all trades Master of one
Thanks to the wonders of online, the Fluke 117 is here.
With the Fluke set to "Auto-V LoZ" (with 3K ohm anti-ghost resistor):
Both circuits Off
B+W 0.0 V
R+W 0.0 V
B+R 0.0 V
Multitester not touching any wires: 0.0 mV
Only # 3 On
B+W 0.1 V
R+W 119.5 V
B+R 0.3 V
Only #13 On
B+W 120.1 V
R+W 0.2 V
B+R 0.2 V
Both #3 and #13 On
B+W 120.1 V
R+W 119.7 V
B+R 239.9 V
Note that the Fluke does not show mV in this mode but 0.1 to 0.2 V = 100 mV to 200 mV, which is in line with yesterday's tests with the Radio Shack meter and the resistor.
With the Fluke set to AC Volts (no anti-ghost resistor):
Both circuits Off
B+W 7.19 V
R+W 0.037 V
B+R 0.558 V
Multitester not touching any wires: 0.0 V (but as high as 0.130 V when near my laptop)
Only # 3 On
B+W 36.69 V
R+W 119.3 V
B+R 72.4 V
Only #13 On
B+W 121.0 V
R+W 45.85 V
B+R 64.93 V
Both #3 and #13 On
B+W 120.2 V
R+W 119.9 V
B+R 240.0 V
So yeah, the Fluke can see the ghost voltage when it's not compensating for it.
If this calculator is correct, it's 47 micro-amps or 0.047 mA. To get up to 5 mA, I'd have to have 16.5 V across 3300 ohms (yesterday's resistor) or 15 V across 3000 ohms (Fluke's resistor). So about 75-100 times more amps than the "dead" circuit is carrying. Am I checking that correctly?
Where exactly are you measuring at. ?
Did you disconnect the Neutral wire that was connected to a breaker ? Where does it go ?
Good Luck.