2nd floor powder room directly over exist. basement full bath

Discussion in 'Plumbing Forum, Professional & DIY Advice' started by baltimorecaesar, Jul 16, 2012.

  1. baltimorecaesar

    baltimorecaesar New Member

    Messages:
    4
    Location:
    Baltimore, MD
    I'm in the process of installing a 2nd floor powder room directly over an existing full bath in my basement which I am also in the process of a gut/remodel as well. The powder room will take the place of an existing closet, so I need to run all new plumbing to service the toilet and sink. I sketched up a diagram of the waste-vent system in CAD to help illustrate what I'm trying to run. All horizontal drains & vents will be sloped at least 1/4" per. foot.

    Thoughts? Suggestions?

    Thanks in advance
    mPR-3D-ISO - Copy.jpg
    mPR-3D-RT-ISO - Copy.jpg
  2. jimbo

    jimbo Plumber

    Messages:
    8,997
    Location:
    San Diego
    No vent can be less than 45º when below 42" above the floor. No inspector will allow a loop vent on that sink. You must tie a proper vent into the vent-to-roof.

    Basically, there is NOTHING in your diagram which will pass code.
  3. Tom Sawyer

    Tom Sawyer In the Trades

    Messages:
    3,224
    Location:
    Maine
    Yep and furthermore that waste line needs to go all the way to the basement and tie in to the lateral there if the "stack" is the vent for the downstairs fixtures.
  4. baltimorecaesar

    baltimorecaesar New Member

    Messages:
    4
    Location:
    Baltimore, MD
    alright, how about this:
    mPR-3D-ISO.jpg
    mPR-3D-RT-ISO.jpg
    Also, there is a separate dry vent for the basement fixtures.
  5. Tom Sawyer

    Tom Sawyer In the Trades

    Messages:
    3,224
    Location:
    Maine
    The lav is not vented
  6. baltimorecaesar

    baltimorecaesar New Member

    Messages:
    4
    Location:
    Baltimore, MD
    The problem is that the wall that the sink is against is an exterior load bearing wall, so I wanted to avoid boring through the wall studs to get the sink vent to the existing vent stack. The only other solution I could come up with, would be to run the sink vent straight up the wall, go through the top plate, tear out the ceiling and T into the vent stack between the 2nd story ceiling and the 3rd story floor (See revised drawings).

    mPR-3D-ISO.jpg
    mPR-3D-RT-ISO.jpg

    Is this better?

    And thanks for the helpful advice all.
  7. Tom Sawyer

    Tom Sawyer In the Trades

    Messages:
    3,224
    Location:
    Maine
    Yep, that be what you need to do to vent the sink properly
  8. baltimorecaesar

    baltimorecaesar New Member

    Messages:
    4
    Location:
    Baltimore, MD
    Cool beans. Thanks again Tom and Jimbo.
Similar Threads: floor powder
Forum Title Date
Plumbing Forum, Professional & DIY Advice Wall mount vs floor mount toilet Aug 28, 2014
Plumbing Forum, Professional & DIY Advice Second floor supply loop routing... Help solve brotherly quarrel. Aug 6, 2014
Plumbing Forum, Professional & DIY Advice How to vent first floor toilet? Which waste line run is best? Jun 24, 2014
Plumbing Forum, Professional & DIY Advice What is the standard reinforcing for at floor joist notched for a tub drain? Jun 15, 2014
Plumbing Forum, Professional & DIY Advice curiosity ... Why are tub drains designed to require a slot in the floor? Jun 15, 2014

Share This Page