The attached diagram shows my setup for a driven shallow well. My question - is the placement of the check valve okay? The well itself is under the house, and the valve placement is the closest I can put it while still having access to it. I am using a Zoeller 3/4 hp jet pump. Thanks!
 

Attachments

  • Well Diagram.pdf
    232 KB · Views: 50

WorthFlorida

6th clinical trail chemotherapy 5/15/24
Messages
5,788
Solutions
1
Reaction score
1,005
Points
113
Location
Orlando, Florida
Cannot open the diagram. What will the well be used for? The check valve can be anywhere from the pump to the well. I prefer it at least a few feet from the pump to allow enough water in the pipe should the well need priming.
 

Mark1400

New Member
Messages
17
Reaction score
3
Points
3
Location
Syracuse, NY
It is the water supply for a house. Check valve is about 6' from where well point comes out of ground, and a few feet from the pump. I pasted the image below.
1714568669273.png
 