At the thermostat base plate. When theres a call for heat the stat closes that contact R to W the base plate is just for wire termination.
Are certain Rc and W1 are the right wires to connect at the base of the thermostat because I’m definitely not certain?

Also, is there any risk of damage to equipment, transfomer, relay, etc?
 

Reach4

Well-Known Member
Messages
38,948
Reaction score
4,457
Points
113
Location
IL
1. no.
2. Since you are skittish, instead of shorting the two terminals, you could read the AC voltage instead. If you see ~24 VAC, that will provide some info. Fitter30 is providing good information.
 

Researcher2

New Member
Messages
23
Reaction score
0
Points
1
Location
Chicago
1. no.
2. Since you are skittish, instead of shorting the two terminals, you could read the AC voltage instead. If you see ~24 VAC, that will provide some info. Fitter30 is providing good information.
I must be misunderstanding what you mean by jumping the terminals because nothing happens when I run a jumper across both wires. I made sure copper was touching on both sides.

1660790224562.png
 

Researcher2

New Member
Messages
23
Reaction score
0
Points
1
Location
Chicago
1. no.
2. Since you are skittish, instead of shorting the two terminals, you could read the AC voltage instead. If you see ~24 VAC, that will provide some info. Fitter30 is providing good information.
@Fitter30 @WorthFlorida
I did confirm that either the old actuator or the new actuator are both ~ 24 VAC. Surprisingly, the new actuator is a bit lower than the old one, but still showing 26 VAC.

Old Actuator Below
1660790402879.png


New Actuator Below (with clicking noise)
1660790442148.png
 
Last edited:

Researcher2

New Member
Messages
23
Reaction score
0
Points
1
Location
Chicago
R u sure the zone valve didn't open? Have 26 vac it should be open. No clicking? Pull a wire at valve should close.
No nothing. I can try again tomorrow.
The specs reads 6 seconds from fully open to close, 4 seconds from fully closed to open.

Now the use of a capacitor makes sense. With a capacitor voltage slowly drops to allow the motor to close the valve since any controller immediately removes power to the actuator. Doubtful that the transformer is short on power. The spec reads 12 zone valves/40VA transformer.

Thermostat wiring is a little strange. Is this the unit you're testing with? Is there 4 or 5 wires? W! is heat and that shout be wired to the actuator. ACC+ is 24v to drive accessories and that is strapped to W1 if this is four wire. Anytime a call for heat or cool, voltage is applied to ACC+. The white seems to loop around or are there 2 white wires. Also, two reds? Is the thermostat near the air-handler so it is easy to run a second wire? I know everything works as is ,I'm just trying to learn things here.
I believe there are 2 reds and 2 whites. It has been a few years, but I think were originally only 4 wires. I added a two wire that came with a red and white wire. I probably should have bought individual wires that were different colors. :-(
 

Researcher2

New Member
Messages
23
Reaction score
0
Points
1
Location
Chicago
With stat subase. Unless that actuator is bad and took out the transformer shouldn't have a problem.
R-C 24v
R- W 0v
R- y 0v
Had to turn off all power (fuses, thermostat, closet switch, etc) multiple times and then compressor started to work about 2am this morning. The compressor is only 3 years old, but has never once had an issue.

Does it matter that the wires go from Rc - W1 and not Rh - W1? Isn't Rc air conditioning.

There are no wires at Rh (under the thermostat to jump).
 

Fitter30

Well-Known Member
Messages
4,403
Reaction score
809
Points
113
Location
Peace valley missouri
Their tied together in the thermostat. You only have one R and it doesn't matter which terminal its landed on. Some really old systems were wired with two transformers one for heat one for cooling. Did the valve stop clicking?
 
Last edited:

Researcher2

New Member
Messages
23
Reaction score
0
Points
1
Location
Chicago
Their tied together in the thermostat. You only have one R and it doesn't matter which terminal its landed on. Some really old systems were wired with two transformers one for heat one for cooling. Did the valve stop clicking?
The relay is still clicking when I hook it up normally. Jumping r - w didn’t charge the actuator.
 

Fitter30

Well-Known Member
Messages
4,403
Reaction score
809
Points
113
Location
Peace valley missouri
R is power 24v to C
w1 1st stage heat
w2 2 stage heat
y1 cooling
look at post 28 its your diagram and its correct
Relay still clicks in heat but in cooling work fine?
 
Last edited:

Researcher2

New Member
Messages
23
Reaction score
0
Points
1
Location
Chicago
R is power 24v to C
w1 1st stage heat
w2 2 stage heat
y1 cooling
look at post 28 its your diagram and its correct
Relay still clicks in heat but in cooling work fine?
Correct, no issues with cool. Only when using the actuator.

Cooling doesn't use the actuator. It a regular AC/Compressor.

Heat is hydronic and therefore requires the actuator to open the valve.
 

Fitter30

Well-Known Member
Messages
4,403
Reaction score
809
Points
113
Location
Peace valley missouri
Theres either a problem with the wiring or programming. Ecobee under furnaces/ boiler - section on fans ,fan should operated by ecobee.
 