How far from a window can a vent stack be? UPC Code

Users who are viewing this thread

Antonio4791

New Member
Messages
11
Reaction score
0
Points
0
Location
South Pasadena CA
Hi all,

I am new here. Hope someone here can answer my question. I am constructing a bathroom within the existing footprint of my home. I am wondering how far from a window a vent stack can be. There is a window nearly directly below where I want to vent. The vent will of course be above the roof, but I need to know how far from the edge of the house it can be. The reason I am concerned is that I have a clay tile roof, which is nearly impossible to walk on. I would like to be install the flashing for the vent by standing on a ladder leaned against the house. But if I get too far away from the roof's edge I cannot do this. Do any codes in California prohibit me from having a vent poke through the roof, say 2-3 feet from the edge of my roof? My city uses California code and doesn't have extra rules.
 

Doherty Plumbing

Journeyman & Gas Fitter
Messages
810
Reaction score
5
Points
0
Location
Penticton, BC
Website
www.facebook.com
Hi all,

I am new here. Hope someone here can answer my question. I am constructing a bathroom within the existing footprint of my home. I am wondering how far from a window a vent stack can be. There is a window nearly directly below where I want to vent. The vent will of course be above the roof, but I need to know how far from the edge of the house it can be. The reason I am concerned is that I have a clay tile roof, which is nearly impossible to walk on. I would like to be install the flashing for the vent by standing on a ladder leaned against the house. But if I get too far away from the roof's edge I cannot do this. Do any codes in California prohibit me from having a vent poke through the roof, say 2-3 feet from the edge of my roof? My city uses California code and doesn't have extra rules.

Someone from your area will probably chime in soon but in most cases you need to be 3' away.
 

Jimbo

Plumber
Messages
8,918
Reaction score
18
Points
0
Location
San Diego, CA
906.1 Vent shal terminate not less than 6" above the roof nor less than 1 foot from any vertical surface.

I interpret "vertical surface" meaning such surface rising above the roof, not the edge of the roof. Never had the occasion, so I don't know if that interpretation is correct.

906.2 Vent shall terminate.....at least 3 feet above any operable door or window.
 