This system is not cooling the way it supposed to cool. It is not getting to the desired temp or just keeps running for a long time when it is really hot.
The system will only turn off after the sun has come down (evenings) or a night.
The system does not have a TXV valve so I tested it via superheat.
- wet bulb temp was around: 63.4
- out door temp was around: 82.4
According to the superheat charging chart, this will be a target super heat of 13.
Then I measured the actual suction line temp and compared it with the saturated temp and this was the outcome:
The actual suction line temp was around: 44.8
The saturated temp was around: 44
The superheat charging chart that I used says the following:
Actual suction line temp - Saturated temp = actual superheat
- If the actual superheat is too high, then add refrigerant
- If the actual superheat is too low, then recover regrigerant
So I guess in this scenario, it needs refrigerant right?
Please see pictures attached.
https://drive.google.com/file/d/1lt5Wb9uIQsidL4vjJMwN24Vwn1d6TEQzTA/view
The system will only turn off after the sun has come down (evenings) or a night.
The system does not have a TXV valve so I tested it via superheat.
- wet bulb temp was around: 63.4
- out door temp was around: 82.4
According to the superheat charging chart, this will be a target super heat of 13.
Then I measured the actual suction line temp and compared it with the saturated temp and this was the outcome:
The actual suction line temp was around: 44.8
The saturated temp was around: 44
The superheat charging chart that I used says the following:
Actual suction line temp - Saturated temp = actual superheat
- If the actual superheat is too high, then add refrigerant
- If the actual superheat is too low, then recover regrigerant
So I guess in this scenario, it needs refrigerant right?
Please see pictures attached.