What your wife wants is no big deal and can be done easily.
Either GFCI protection from the breaker or where the first receptacle lands physically in the kitchen.
You can run two separate circuits to the kitchen either by two single pole breakers 12/2 with ground
or MWBC (shared neutral) to the first landing receptacle location. You can also since running two separate circuits or MWBC whichever bring both to a double duplex side by side in the same 2 gang box. This way she has the ability to plug in two different appliances one on each of the two duplex receptacles and on each one still have an available place to plug in something less power hungry such as a phone charger etc. Then you have less need for a power strip, pulling one plug out and putting another one in due to lack of plug space. Then you can run those two circuits to another double duplex 2 gang box and so on.
The advantage of running more than one circuit to the counter tops and alternating their locations (or adding locations) is that if one of the circuits fail and you only have one circuit to the counter tops you don't have to run an extension cord or if you have one circuit on one side of the sink and another on the other side of the sink with multiples to them on the same sides and the circuit goes dead you have to shift all your countertop appliances to one side of the sink to be able to use them until you can gt someone in the check the reason for the failure.
Unless you really need to have a MWBC I would run single 120v circuits (20amps). Again so if there is an issue with a circuit and you as a DIYers can't solve it on your own you have other working receptacles along the entire length of the countertop. This is what I always did when running circuits on countertops. Code only required 2 SABCs but I tried hard to convince the home owner or contractor/landlord etc to run several. An entire countertop without power the landlord will be swamped with calls from the tenant until it is fixed. If only one receptacle goes dead on the countertop the tenant has several other receptacles to use; far less inconvenient far less calls from the tenant or yelling from the "wife".