Whirlpool Wiring

Users who are viewing this thread

pitteach

New Member
Messages
27
Reaction score
0
Points
0
Location
Hamburg, NY
I am preparing to wire a whirlpool tub (no heater, 1/2 hp) and I have a couple of questions:

1. The instructions call for a dedicated 12/2 feed which is what I will do. Can I use regular romex under the tub or should I use an exterior type in case of wetness?

2. GFI: Should I use a receptacle to plug in under the tub, or use the GFI at the panel, or both? I suppose I prefer to use the breaker so I can hard wire and seal everything under the tub.

I also plan on wiring the tub to a wall switch so the kiddies can't mess with the jets during a bubble bath.

Thanks.
 

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,770
Reaction score
1,190
Points
113
Location
New England
Regular romex should be fine...just like anything else, that is supposed to be a dry area. The wet stuff is required if it is expected to get wet.

I think you'll be happier if the gfci is in the panel since it would not be a major pain to get to if it ever did trip. Plus, you are supposed to check it on a periodic basis which would never happen if it was burried beneath the tub.

Just make sure that the switch you select is rated for the 20A supply, and it should be fine. Most wall switches are only rated for a 15A load, so you may have to go to an electrical supply...depends on where you are looking.
 

Chris75

Electrician
Messages
607
Reaction score
0
Points
0
Location
Litchfield, CT
Just make sure that the switch you select is rated for the 20A supply, and it should be fine. Most wall switches are only rated for a 15A load, so you may have to go to an electrical supply...depends on where you are looking.

Why would he need a 20 amp switch? I highly doubt that motor draws more than 10 amps,
 
Last edited:

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,770
Reaction score
1,190
Points
113
Location
New England
Shouldn't the switch handle the full load of the single item it is connected to? A 20A circuit, a 20A switch? I'm just guessing here, but wouldn't that be the same as putting 14g wire to extend a 20A circuit?
 

JWelectric

Electrical Contractor/Instructor
Messages
2,608
Reaction score
21
Points
38
Location
North Carolina
I am preparing to wire a whirlpool tub (no heater, 1/2 hp) and I have a couple of questions:

1. The instructions call for a dedicated 12/2 feed which is what I will do. Can I use regular romex under the tub or should I use an exterior type in case of wetness?
Yes Nonmetallic cable can be used.

2. GFI: Should I use a receptacle to plug in under the tub, or use the GFI at the panel, or both? I suppose I prefer to use the breaker so I can hard wire and seal everything under the tub.
either or would work but you can't cut the cord and hard wire the tub.

I also plan on wiring the tub to a wall switch so the kiddies can't mess with the jets during a bubble bath.

Thanks.
This will be fine and a 15 amp switch will be just fine should you decide to use one.

You could not spoil the child and use the rod instead of the switch.
 

hj

Master Plumber
Messages
33,602
Reaction score
1,041
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
gfci

I would mount a GFCI outlet in the spa's vicinity and then run from its load terminal to the concealed outlet. That puts the reset within reach if it trips, and makes it more likely to be tested, rather than if it were inside the panel where no one ever goes unless to reset a breaker.
 

Chris75

Electrician
Messages
607
Reaction score
0
Points
0
Location
Litchfield, CT
I would mount a GFCI outlet in the spa's vicinity and then run from its load terminal to the concealed outlet. That puts the reset within reach if it trips, and makes it more likely to be tested, rather than if it were inside the panel where no one ever goes unless to reset a breaker.

This is a state amendment in Connecticut, you cannot place a GFCI inside the tub area. They feel you wont test the GFI every month if its buried behind a panel. You can install a GFI breaker, which is what I always do anyway. You dont want to be changing out a gfi receptacle under a tub after the fact...
 