Whats Minimum distance of ptrap to santee?

Users who are viewing this thread

Nanmer

New Member
Messages
13
Reaction score
0
Points
1
Location
Texas
Does anyone know whats the minimum distance between the ptrap to santee that is in a vertical position in ipc code? I think upc is 2 times pipe diameter can't find ipc minimum.
 

Reach4

Well-Known Member
Messages
33,210
Reaction score
3,275
Points
113
Location
IL
IPC 906.3 Crown Vent. A vent shall not be installed within two pipe diameters of the trap weir.
 

Nanmer

New Member
Messages
13
Reaction score
0
Points
1
Location
Texas
IPC 906.3 Crown Vent. A vent shall not be installed within two pipe diameters of the trap weir.
So,does that mean that anything within the two pipe diameters is called a crown vent?
 

Nanmer

New Member
Messages
13
Reaction score
0
Points
1
Location
Texas
Somebody else please chime in.
So,does that mean that when your venting a ptrap anything within the two pipe diameters is called a crown vent? I say yes. Doesn't matter if its the tee in the vertical or tee in its back.
 