What water supply flow rates should I maintain for my home

Users who are viewing this thread

Curious Skip

Member
Messages
34
Reaction score
4
Points
8
Location
NC
I did a little updating since last post. New expansion tanks on both the boiler and the AO Smith WH. The old tank on the AO Smith was full of water, held up by just the plumbing. The pressure now caps out at 54, where it was almost 80.

WH1b.jpg
WH 3b.jpg
 

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,771
Reaction score
1,191
Points
113
Location
New England
Personally, I prefer to size the tanks such that they do not exceed the 80-psi under worst case scenarios. Varying the pressure causes stress on things, including your WH tank, and things like washing machine hoses. The porcelain lining doesn't like it when it gets stressed. The WH is tested to 300psi, so won't burst, but that doesn't mean repeated stress to the lining can handle it. A bigger ET is cheap compared to replacing a WH earlier than needed.

A bypass PRV is mostly a waste of money and one more thing that can fail today, especially if you have that high of inlet pressure. The bypass can only open when the house side exceeds the supply. If it got to 150psi, the WH's TPR will open, or at least should. Plus, most utilities either now have, or will be installing check valves, so there's no place for that bypassed valve to let water go, either.

The more an ET bladder stretches, the shorter its lifespan. The tank manufacturers don't particularly care as long as it makes it through the warranty period.

Do what you want, upsizing the tank is cheap all around. ONe leaking WM hose could cost thousands.
 

Curious Skip

Member
Messages
34
Reaction score
4
Points
8
Location
NC
Personally, I prefer to size the tanks such that they do not exceed the 80-psi under worst case scenarios....

Do what you want, upsizing the tank is cheap all around. ONe leaking WM hose could cost thousands.

It was this advice that I followed....this is a 4.5 gal tank. Much less stress on the system. I also listened to Reach4 and made sure the new tank was well supported. I was amazed at how heavy the old tank was....with no support beside the copper plumbing.
 