City water you had better make sure you have nothing dripping as your paying for every drop you use
Also running up to 325 feet you will need a minimum pressure 141 PSI to get a trickle of water that high
Then there is the required pressure needed to overcome friction losses and what the min pressure you will need for showers , sprinklers etc
When doing high rise buildings we get the height of the upper most floor and times it by .433 to get the static pressure
In your case 325 feet X .433 = 140.75 PSI that is just static no flow
If you take 140.75 PSI times 2.31 you end up back to 325 feet and then we add in a fudge factor such as flushometers ned over 25 PSI and min for faucets is around 8 PSI
Do you have a hot water boiler? If so then you need to calculate the highest radiator / baseboard and make sure they have at least 4 PSI cold fill
A lot of localities frown upon a suction pump as it can draw water out of the city main especially when needed to fire fighting
Then there is the worry about possible frost line and velocity causing erosion in ferrous and non ferrous metal piping
85 PSI will only elevate water 196 feet
FYI 85 PSI = a velocity of 32 FPS (full flow)
Using 85 PSI and 11/2 pipe diameter would be 180 GPM (not including the pressure losses )
one cannot just arbitrarily pick a pipe size and then wonder about pressure tanks and what code officials might say as your so HIGH above the main I am sure they will want air gaps or the very least backflow prevention