Hi all,
We just bought a house with a Weil Mclain WTGO-3 115k BTU Output Gold Oil Boiler w/ Tankless Heater and baseboard heating and have been struggling to understand why the system has two expansion tanks. The smaller expansion tank adjacent to the boiler is a Therm-X-Trol ST-5 (2 gallon). It appears to feed into the boiler (pipe feeds into an inlet named "in" on the boiler. The larger expansion tank above the boiler is a Extrol Model 60 (7.6 gallon). The system also feeds the domestic hot water supply and after reading through the boiler manual, I can't find anything that talks of 2 expansion tanks being needed (unless being used with a refrigeration system - which it is not).
The smaller tank is currently full of water and sprays pressurized water when trying to test it with a pressure gauge. As a result, I'm thinking this is why the boiler is reaching 33psi during operation and leaking from the boiler relief valve.
I would greatly appreciate any help with the following questions to try and help me understand the importance of this smaller tank.
1, What is the purpose of this smaller tank if a larger one exists on the system?
2, What is the purpose of the line the smaller tank is on that feeds into the boiler?
3, If replacing the smaller tank (2 gallon), can I use a 4 gallon (designed for boilers) or should we upgrade the larger tank?
4, What PSI should the replacement tank be set at? Should it match the incoming water pressure or be left at 12 PSI pre-charge?
Thank you!
We just bought a house with a Weil Mclain WTGO-3 115k BTU Output Gold Oil Boiler w/ Tankless Heater and baseboard heating and have been struggling to understand why the system has two expansion tanks. The smaller expansion tank adjacent to the boiler is a Therm-X-Trol ST-5 (2 gallon). It appears to feed into the boiler (pipe feeds into an inlet named "in" on the boiler. The larger expansion tank above the boiler is a Extrol Model 60 (7.6 gallon). The system also feeds the domestic hot water supply and after reading through the boiler manual, I can't find anything that talks of 2 expansion tanks being needed (unless being used with a refrigeration system - which it is not).
The smaller tank is currently full of water and sprays pressurized water when trying to test it with a pressure gauge. As a result, I'm thinking this is why the boiler is reaching 33psi during operation and leaking from the boiler relief valve.
I would greatly appreciate any help with the following questions to try and help me understand the importance of this smaller tank.
1, What is the purpose of this smaller tank if a larger one exists on the system?
2, What is the purpose of the line the smaller tank is on that feeds into the boiler?
3, If replacing the smaller tank (2 gallon), can I use a 4 gallon (designed for boilers) or should we upgrade the larger tank?
4, What PSI should the replacement tank be set at? Should it match the incoming water pressure or be left at 12 PSI pre-charge?
Thank you!