The UFTC-140 has 4 gallons/ 33lbs of water in just the heat exchanger (distinct from the one gallon domestic hot water tanklet) compared to about 11lbs for the AB-120.
UFTC-140 combis also have an internal primary pump and MUST be plumbed primary/secondary on the heating side (unlike the UFT heating boilers), despite the low-head heat exchanger, though you could probably cheat that if you run the math on heating system loop's pumping head, using ONLY the internal pump (set to 3, it's maximum speed), given that it's one zone and probably fairly low head. The manual for the Westinghouse branded version of the UFTC-140 lives here. I believe they're identical under the paint, but the manual for the UFTC-140 appears to be updated and slightly different. It's worth looking over both manuals for figuring out the system design. In a quick scan I didn't see a maximum length specified for the length of plumbing between the boiler and the closely spaced tees hydraulic separator, but maybe it's in there. (Look for it.)
There is no particular advantage to wall mount vs. floor mount versions. The wall mount units are usually cheaper, but not by much when factoring in the cost of the wall-bracket for mounting it.
If 87% efficiency is acceptable cranking it to ~155-160F out on 27' of baseboard would guarantee nearly continuous burns during calls for heat without buffering. The max space heating output temp on the thing is 180F, so you really CAN get there without buffering, but you can also probably inch it down into the higher temp end of the condensing zone on space heating calls without short cycling it:
With even 50 feet of 3/4" plumbing + fin-tube you'd be looking at another 8 lbs of thermal mass beyond the 33lbs of water in the heat exchanger. Assuming so with ~50lbs total mass to work with, an output temp of 140F, AWT of 135F the 27 fin tube would be emitting ~8100 BTU/hr and running at close to 90% efficiency. At 90% efficiency the UFTC-140 would be delivering 12,600 BTU/hr into the system, for about 4500 BTU/hr ( = 75 BTU/minute) of excess heat into the system. With 50 lbs of thermal mass to work with the temperature would be slewing 75BTU/50lbs= 1.5F per minute, so it's highly likely you'd be able to get at least 3 minutes of minimum burn time out of it without external buffers.
The differential temperature between burner-off and burner-on doesn't seem to be programmable (it might be- read the programming details in the manuals), so the minimum temperature before it short-cycles may have to be determined empirically. With 3+ minute burns and much fewer than 10 burns/hour during continuous calls for heat (<5 burns would be better) it won't be putting huge amount of wear and tear on the boiler.
UFTC-140 combis also have an internal primary pump and MUST be plumbed primary/secondary on the heating side (unlike the UFT heating boilers), despite the low-head heat exchanger, though you could probably cheat that if you run the math on heating system loop's pumping head, using ONLY the internal pump (set to 3, it's maximum speed), given that it's one zone and probably fairly low head. The manual for the Westinghouse branded version of the UFTC-140 lives here. I believe they're identical under the paint, but the manual for the UFTC-140 appears to be updated and slightly different. It's worth looking over both manuals for figuring out the system design. In a quick scan I didn't see a maximum length specified for the length of plumbing between the boiler and the closely spaced tees hydraulic separator, but maybe it's in there. (Look for it.)
There is no particular advantage to wall mount vs. floor mount versions. The wall mount units are usually cheaper, but not by much when factoring in the cost of the wall-bracket for mounting it.
If 87% efficiency is acceptable cranking it to ~155-160F out on 27' of baseboard would guarantee nearly continuous burns during calls for heat without buffering. The max space heating output temp on the thing is 180F, so you really CAN get there without buffering, but you can also probably inch it down into the higher temp end of the condensing zone on space heating calls without short cycling it:
With even 50 feet of 3/4" plumbing + fin-tube you'd be looking at another 8 lbs of thermal mass beyond the 33lbs of water in the heat exchanger. Assuming so with ~50lbs total mass to work with, an output temp of 140F, AWT of 135F the 27 fin tube would be emitting ~8100 BTU/hr and running at close to 90% efficiency. At 90% efficiency the UFTC-140 would be delivering 12,600 BTU/hr into the system, for about 4500 BTU/hr ( = 75 BTU/minute) of excess heat into the system. With 50 lbs of thermal mass to work with the temperature would be slewing 75BTU/50lbs= 1.5F per minute, so it's highly likely you'd be able to get at least 3 minutes of minimum burn time out of it without external buffers.
The differential temperature between burner-off and burner-on doesn't seem to be programmable (it might be- read the programming details in the manuals), so the minimum temperature before it short-cycles may have to be determined empirically. With 3+ minute burns and much fewer than 10 burns/hour during continuous calls for heat (<5 burns would be better) it won't be putting huge amount of wear and tear on the boiler.