I just bought a home with a submersible pump and 32G Amtrol-Well-X-Trol tank. Pump turns on @ 32 PSI, runs for only short time and turns off. Pressure increases on gauge until 40PSI, quickly jumps to 60PSI and then turns off. Pressure then drops to 40PSI until water is used at any faucet. What causes the rapid jump in pressure? thanx in advance for your advice.
1. How far separated are your pressure gauge, pressure switch, and pressure tank?
Pump turns on @ 32 PSI, runs for only short time and turns off. Pressure increases on gauge until 40PSI, quickly jumps to 60PSI and then turns off.
2. runs for what-- 10 seconds? Does the pressure gauge rise to 40 before the pump turns off or a while later?
3. Is the pressure switch new, what is it supposed to be (30/50 psi?), and did you adjust it?
If you have a 30/50 pressure switch, you should adjust the air precharge to 28PSI. Precharge is always measured and adjusted with the water pressure at zero. I am not sure of your symptoms. If the precharge was at 38 PSI, I would expect the pressure to rise to 38 or 40 very quickly.
I am suspecting that either your pressure switch and pressure gauge are not together or something is clogged. The old nipples may have deposits that keep the gauge from seeing the pressure for a while. If the gauge and switch and pressure tank are not together, I would make them so. I would clean out or replace any old pipe nipples.
You might post a picture of the pressure switch, pressure gauge and pressure tank inlet area if you can get them in the same picture.