As long as you fill the system when the pump isn't running it doesn't matter
at all where the feed point is relative to the expansion tank or pump.
But it's a bad idea to feed cold water into a hot system right at the cast-iron casting, where it might enter a hot boiler at a radically different temperature, which puts the heat exchanger plates under considerable mechanical stress, and can even crack a plate. It's better to put it on the plumbing on the output side of the boiler, not on the boiler itself. If the feed is right at the boiler, only fill the system when the system is cool or tepid, say under 100F.