Dave, you said "See my thread below with quote my water was just tested". I interpreted that to mean a water report was included within the quote PDF document.
there was it was only ph, hardness and ironDave, you said "See my thread below with quote my water was just tested". I interpreted that to mean a water report was included within the quote PDF document.
can a back flow preventer be used as a vacuum breaker?there was it was only ph, hardness and iron
So that says it then no booster pump then. So i noticed my water treatment company that installed this originally put a 7GPM check valve before the ultrafilter and a 10GPM check valve after then the pressure reducing valve to the booster pump. Could those devices possibly saved my water treatment or i guess it could be crushed its been running this way since 2016. The water treatment company that went under sold to culligan so of course all my warranties are null and void and i have no way to sue them. So they are coming out thursday to check the system and see what it is and bring the "manager" as well. I can only figure what this means, they come out say yeap its done but here we want to sell you the culligan proprietary solution. The well company that quoted me waived all labor because they felt bad and to their respect it was honorable but i know those prices i was given are marked up big time.Even if the booster does not collapse the media tank, it could crush the bottom basket which would create a significant flow restriction.
I don't see that.Even if the booster does not collapse the media tank, it could crush the bottom basket which would create a significant flow restriction.
No booster pump after the filtering, unless you supplement that with a vacuum breaker to prevent the potential tank collapse.So that says it then no booster pump then.
A vacuum breaker admits air. Some backflow presenters admit air, but the ones for hoses have a tendency to leak. SThe term backflow preventer is not very specific. The vacuum breakers often used with upper story water heaters are readily available.can a back flow preventer be used as a vacuum breaker?
I don’t understand how a booster pump after the softener could possibly help improve water flow and pressure when there is not adequate flow through the softener. As you are making adjustments — it might be possible to add some pressure gauges (question for the experts — not sure how much additional pressure drop would occur from the gauges), those would help monitor the system and pinpoint issues.I don't see that.
No booster pump after the filtering, unless you supplement that with a vacuum breaker to prevent the potential tank collapse.
A vacuum breaker admits air. Some backflow presenters admit air, but the ones for hoses have a tendency to leak. SThe term backflow preventer is not very specific. The vacuum breakers often used with upper story water heaters are readily available.
Not sure I understand. You have the same setup and don't see that or you disagree?I don't see that.
So let me ask this a vacuum breaker resolves any issues of fouling the filtration equipment correct? Then i can use a pump after the equipment? Heres my idea:Not sure I understand. You have the same setup and don't see that or you disagree?
The force exerted on the bottom basket increases when there is a large pressure differential across the equipment which was the reason the booster pump was installed to begin with. The pressure drop is a combined friction loss of all components in series. The lower basket is near the end of the series resistors so likely to see more differential than any component after it.
I don't have a booster pump. What I don't see is how a booster pump after a softener or backwashing filter crushes a bottom basket.Not sure I understand. You have the same setup and don't see that or you disagree?
Since i had much better water pressure with the inline booster pump installed (franklin electric inline 400) i want to put it back in. You mentioned vacuum breaker, i see a bunch out there and i bought one to install however, i am concerned about this thing. Apparently it will leak some water from the point where the air break occurs and it needs to be near a drain so that has me worried about how much water and how often this might happen? Also is this the right device you are suggesting? If so i plan to put it 12" above the pump level like it says in the instructions see the link below for specs and what i purchased. Will this resolve the issue of crushing my tanks? Or can i use a double check valve instead? The reason i mention double check valve is because the risk of property damage with the vacuum breaker that thing does emit water out of the cap....Always install a vacuum break between a pump and any treatment tanks. Collapsed tanks are really neat to look at. https://view.publitas.com/impact-water-products/2018-catalog-final/page/140-141
Before we can make any recommendations you need to get a real laboratory test. Water treatment should not be that difficult. As to determining which tank it is, if you have Autotrols and your water guy has even a little bit of experience (sounds like he may be lacking) he would know that you can simply push the bypass valve open to see if that corrects the pressure drop.
View attachment 61976
Is that basically the same as the one i bought https://www.ferguson.com/product/zu...ker-w420xlg/_/R-4238922?searchKeyWord=w420xlg ?You could use something like https://www.ferguson.com/product/wa...lve-wlfn36m1f/_/R-3920150?searchKeyWord=lfn36 unless the two ports or 1 inch thread would make it easier for you.
So what your saying is instead of using a vacuum breaker, use a check valve? I have this one if this will do the same thing? https://www.ferguson.com/product/wa...f7ru22fd/_/R-4525740?searchKeyWord=wlf7ru22fdInteresting solution, use a ball check on a tee, 1/2" should be fine, these break with almost no negative pressure. You can also attach a tube to the other side and run it to a drain. https://www.mcmaster.com/4721k14
This is awkward, but...