We recently moved into a new home (our first) and are experiencing living with a well and softener for the first time, so sorry if I don't know the terminology correctly yet.

When we moved in, the toilets were stained yellow/brown, the dishwasher had a white powdery coating all over the inside, the shower stall has gradually turned brown/orangish and worst of all my wifes blonde hair is starting to turn orange :eek: (not a happy camper!) I scrubbed out the dishwasher with CLR and same with the toilets. Dishwasher seems to be holding up fine, but toilets start to get a stain after a week or 2

We had a plumber come out on 1/6 to diagnose, but it is now the 24th and hasnt returned any of my phone calls, so I'm looking to see if this is something I can do on my own or gather enough imformation to have someone else fix this.

From the septic report: Well drilled 2002 is 185 feet deep, more than 38 feet of protective clay above the aquifer. The well is 5 inches in diameter with plastic casing and a submersible pump, property screened vented and 12" above grade. They did not run a hardness/iron test

The previous owners had the following test:
November 2005 Routine Test
Sampling Point: Kitchen Tap
Hardness result: 52, detec limit: 30, unit: mg/L
Iron result: 0.1, detec limit: 0.1, unit mg/L

And when the plumber we hired to take a look came out:
January 2009 local plumber notes:
untreated (before softener) 1-ppm Iron, 18-gr hard
treated (after softener) 0.8-ppm Iron, 18-gr hard

He said the head is operating properly, hardness set to 30 and regens daily, salt is being used to no effect (no clumping found, he said not to fill it up so high though in the future), and found media in the water heater

The water pressure was set to 40/75, he said normal is 40/60 and the high pressure might have 'blown out' the media in the softener.

On the back of the head of the softener it says "Pressure 20-125" so I'm not sure that 75 psi could really blow out the media as he said or not.


At the time of service, he could not get the head off of the unit to look inside the softener tank (the one that you dont put salt pellets into)


I couldnt find what the model number is, but the manual says "WaterLover's Series 1" Metered Control" and here are some pictures with any numbers I could find on it


System
http://img132.imageshack.us/img132/3514/img2783largehj0.jpg

Brine tank
http://img502.imageshack.us/img502/2070/img2779largeek4.jpg
http://img405.imageshack.us/img405/8228/img2780largezh7.jpg

Softener Head
http://img300.imageshack.us/img300/8140/img2790mediumdj8.jpg
http://img299.imageshack.us/img299/1294/img2789largesf5.jpg
http://img300.imageshack.us/img300/351/img2788largerx4.jpg
http://img405.imageshack.us/img405/7159/img2787largesl6.jpg
http://img502.imageshack.us/img502/4377/img2786largend2.jpg


If there is any other information I can provide or try to search for, let me know

Thanks for any guidance/help

-Rick
 

Sammyhydro11

In the Trades
Messages
708
Reaction score
1
Points
16
Location
Massachusetts
If he found media in the water heater, then the machine lost some of its resin, which would reduce its capacity. Did he check to make sure it was drawing brine? If it lost media then it should be determined why and also the amount lost should be replenished. Did he set the pressure back to 40/60? There is a guy here named Gary Slusser that specializes with that valve and i'm sure he will give you some good info on it.

sammy

www.tylerwellandpump.com
 

rschmitty

New Member
Messages
17
Reaction score
0
Points
1
Location
Indiana
If he found media in the water heater, then the machine lost some of its resin, which would reduce its capacity. Did he check to make sure it was drawing brine? If it lost media then it should be determined why and also the amount lost should be replenished. Did he set the pressure back to 40/60? There is a guy here named Gary Slusser that specializes with that valve and i'm sure he will give you some good info on it.

sammy

www.tylerwellandpump.com

I don't recall if he did or not. He did not say to me that it wasn't drawing brine..but obviously doesnt mean he checked. Not sure if this is related or not, but after he left a while later my wife went to get a drink and took a big gulp of salt water. We ran all the faucets for about 10min and the salt taste didnt come back (and hasnt since)

Is there a test I can do to verify this is drawing brine?

When someone says media, is that the same thing as resin or is 1 a subset of the other?

He did reset to 40/60 (the guage reads ~64 when it stops pressurizing)

http://www.clackcorp.com/valve/Manuals/V3115_WS1_1.25.pdf
This is the manual for that unit. Sounds to me that the unit has lost the resin. You have to unscrew the valve from the tank in order to check the resin height. It should be about 2/3 the height of the tank.

Thanks for the manual link!

The valve that connects downward to the tank is really stuck on there, looks like some buildup or something. He could not get the head off to check the tank. I havent tried my self, but incase I fail too, any tricks to loosen up the head?
 

Sammyhydro11

In the Trades
Messages
708
Reaction score
1
Points
16
Location
Massachusetts
If you had salty water then the machine is drawing brine, he probably ran the unit through a cycle manually and didn't rinse the brine out. I'm not familiar with those valves but it looks familiar to a fleck set up but the piston is horizontal than vertical. Anyway, to remove the head it looks like there are two union type fittings that need to be removed. Put the machine on by pass and then place it in regeneration mode to relieve the pressure. Then undo the union female fittings, remove the drain line by un threading the the female fitting that connects the line to the head. Next grab the neck of the head and turn it counter clockwise. It should loosen up. When you get it un threaded be careful when lifting it off the head so you don't pull the distributor up with it.

Until Gary pops in and helps you, that is the best i can tell you.

sammy

www.tylerwellandpump.com
www.tylerwellandpump.com
 

rschmitty

New Member
Messages
17
Reaction score
0
Points
1
Location
Indiana
unit is operating in the correct direction. waiting on a second pair of hands to help try to get head off still



I took some pictures from unscrewing a sink faucet and letting some water out at high speed from the bottom of the tank. I had thought 'media' was round balls, but this looks flakey to me. Could I even be losing resin? Also the plumber seemed alarmed that I was at 40/75 for my water pressure but the system is rated up to 125 psi...

http://img144.imageshack.us/img144/3223/faucetmy0.jpg

http://img301.imageshack.us/img301/3228/waterheaterej7.jpg
http://img405.imageshack.us/img405/6888/waterheater2cp9.jpg
 

Gary Slusser

That's all folks!
Messages
6,921
Reaction score
22
Points
38
Location
Wherever I park the motorhome.
Website
www.qualitywaterassociates.com
You have a Clack WS-1 control valve on what looks like a 1.0 cuft foot softener. That's probably too small for yuor water quality, family size and peak demand gpm of the house.

You should not have your water pressure above say 65 psi. High psi, like 65, means the water flow's velocity through the softener is too fast for the ion exchange and you run the risk of causing water hammer which is capable of causing damage to the softener and other appliances and plumbing and fixtures. It may have broken the distributor tune inside the resin tank. I think you have resin getting out of it. I don't agree wit the prefilter you have in front of the softener, that will rob flow and pressure from the softener and that will cause the resin to fail which I think it probably has. The flat pieces in your pictures may be flaking off the inside of the resin tank, control valve and plumbing.

Any odor to this water and if so, hot cold or both?

You won't get the control off the tank without the distributor tube being pulled up off the bottom of the tank, and then you have to put it back by laying the tank down or you run the risk of breaking the bottom basket and dumping all your resin into the plumbing.

The water in the salt tank has been very high, it could be going that high every regeneration and if it is the salt dose is probably not set correctly.

I think the programming is probably not set right.

Who did you buy the unit from?
 

rschmitty

New Member
Messages
17
Reaction score
0
Points
1
Location
Indiana
No idea who installed it, no name or contact was left on the unit or in any paperwork that came with the house. House was built 2001 so I'd imagine this unit was in shortly after.

Well I finally was able to get the head off with a friends help and a few good hits. I couldnt see any resin at all down inside.

Called a different plumber who was able to bring out some resin and fill it back up. He drained the tank and just very trace ammouts of resin here and there but really it was just water. He shortened the turbulator by a few inches so it was 10 inches total from the top, and installed an upper basket to also prevent resin from being siphoned out. He said shortening the turb will cause some loss of capacity but the factory recommends 10inches.

It was actually a 1.25 tank, he thought 1.0 too but the 1.0 resin bag didnt fill it up. Does that sound too small still? After resin and reprogramming (they had jacked it up to daily regen and set at 40 hardness) he tested the water and it was down to 1. Its now set to 1000 gallons or 7 days for a regen, he said the unit could be extended to a longer regen like 12 or 14 days but with the high hardness he didnt recommend it

I'm no good with smells, but after my wife's first shower she said it no longer has an odor (I was like what odor?? I didnt know we had a smell) I'll ask if she smelled it prior to the fix with cold water too. edit: She said it smelled like sulfur and a metal iron/copper smell before. What does the smell indicate?


Should I just remove the prefilter, it's extruded carbon, not sure what it does exactly other than cost money for filters :)
 
Last edited:

Gary Slusser

That's all folks!
Messages
6,921
Reaction score
22
Points
38
Location
Wherever I park the motorhome.
Website
www.qualitywaterassociates.com
You need to fire the plumber, he doesn't know softeners. Water treatment dealers do.

There are very very few softeners that have the resin tank filled with resin, and yours is not one of them. There should be a freeboard space above the resin, so your tank, probably a 9" x 48" tank, should have empty space of like 15-18.

A Turbulator is a distributor tube that goes from up inside the bottom of the control valve to the bottom of the resin tank. You can not use gravel underbed with a Turbulator tube. Your distributor tube, Turbulator on regular has to be cut off flush with the top of the tank +/- 1/2" with your control valve (Clack WS-1). So he should not have cut anything off a Turbulator or regular dist. tube.

The top basket will keep the resin in the tank mostly but, 'fines' and broken bead pieces can usually get through them, so you may still get resin in your plumbing IF your softener is connected backwards. Otherwise where did all your old resin go, the only place is out the drain line during backwash BUT, then you wouldn't have it in your plumbing. See the problem here?

Also, your softener, like most, does not remove or reduce H2S gas (rotten egg or sulfur smell).

Here's a picture of a Turbulator distributor tube.
 

Attachments

  • Turbcloseup.jpg
    Turbcloseup.jpg
    6.9 KB · Views: 2,925