Hi all. I am getting ready to drywall the laundry room next week. The water main enters the house through the slab as pictured. Several years ago, the old gate valve was replaced prior the water company upgrading the water meter. That valve was replaced by a professional plumber. There is another old gate valve downstream from the water meter.

I would like to drywall as much as possible, but I do realize that I will need to create some sort of box over the area in order to cover it up or make it look finished.

My questions are as follows:

1) Does that old gate valve still need to be there considering there is a ball valve on the city side of the water meter? I know the new valve works as there has been a lot of copper lines run for the remodeling that is in progress.

2) If the valve needs to be there, would you replace it with a new valve or just leave it as is?

3) If it needs to be replaced, I would like to move it lower or closer to the water meter. Any suggestion on location?

I have attached a few pics to help.

Thanks!
 

Attachments

  • IMG_6109 (1).jpeg
    IMG_6109 (1).jpeg
    83 KB · Views: 121
  • IMG_6108.jpeg
    IMG_6108.jpeg
    100.4 KB · Views: 111
  • IMG_6107.jpeg
    IMG_6107.jpeg
    83.1 KB · Views: 109
  • IMG_6106.jpeg
    IMG_6106.jpeg
    87.1 KB · Views: 126

Basilisk

New Member
Messages
11
Reaction score
2
Points
3
Location
Austin, TX
I would be extremely surprised if a homeowner-side shutoff valve is not an absolute must when on city water, especially in IL, that is not exactly famous for its lax plumbing code.
You can't drywall in an existing valve, even if you don't intend to ever operate it, as it needs to be accessible. If I were you, I would put the new shutoff right after the first 90 after the meter, i.e. where you are holding the tape measure on the photo, and just drywall normally. The valve would remain accessible this way. I see that there's a coupling right after that elbow, so I personally would replace the entire section from the old gate valve to the grounding clamp, and use a street elbow to bring the shutoff further away from the future drywall. By the looks of it, everything should fit, a 3/4" sweat x sweat ball valve is less than 3 inches long. So, you'll need a valve, 2 couplings, 1 regular elbow and 1 street elbow (and pipe, of course).

Disclaimer: not a professional plumber
 

Potatoes

New Member
Messages
17
Reaction score
2
Points
3
Location
Lombard, IL
I would be extremely surprised if a homeowner-side shutoff valve is not an absolute must when on city water, especially in IL, that is not exactly famous for its lax plumbing code.
You can't drywall in an existing valve, even if you don't intend to ever operate it, as it needs to be accessible. If I were you, I would put the new shutoff right after the first 90 after the meter, i.e. where you are holding the tape measure on the photo, and just drywall normally. The valve would remain accessible this way. I see that there's a coupling right after that elbow, so I personally would replace the entire section from the old gate valve to the grounding clamp, and use a street elbow to bring the shutoff further away from the future drywall. By the looks of it, everything should fit, a 3/4" sweat x sweat ball valve is less than 3 inches long. So, you'll need a valve, 2 couplings, 1 regular elbow and 1 street elbow (and pipe, of course).

Disclaimer: not a professional plumber
I like how you are thinking. I didn’t look into the exact parts to get so thanks for that. Ideally I would like to put the valve after the first 90, but at first glance I didn’t see how the new valve would fit inside the space in front of the drywall.

Aside from the valve fitting solely in front of the drywall, I assume I would replace everything left of the brass nipple which has a clear plastic zip tie on it. It looks it’s all copper after the brass nipple. It looks like they are using some form teflon paste on the joint where the brass nipple joins with the copper female fitting.
 

WorthFlorida

Clinical Trail on a Cancer Drug Started 1/31/24. ☹
Messages
5,754
Solutions
1
Reaction score
994
Points
113
Location
Orlando, Florida
Gate valves notoriously like to break after closing then opening the valve then stem breaks. Replace it with a good brass ball valve. Having the shut off after the meter prevents the entire home from draining if the meter ever had to be serviced or replaced.
 
Last edited:

Reach4

Well-Known Member
Messages
38,858
Reaction score
4,428
Points
113
Location
IL
Gate valves notoriously like to break after closing then opening the valve the stem breaks. Replace it with a good brass ball valve. Having the shut off after the meter prevents the entire home from draining if the meter ever had to be serviced or replaced.
That whole-house inside valve also provides an accessible place to turn off the water, in case a pipe etc breaks.
 

Potatoes

New Member
Messages
17
Reaction score
2
Points
3
Location
Lombard, IL
That whole-house inside valve also provides an accessible place to turn off the water, in case a pipe etc breaks.
Agree. That’s how I have been turning off the water to run copper. Haven’t even touched the gate valve.
 

Jeff H Young

In the Trades
Messages
8,893
Reaction score
2,221
Points
113
Location
92346
Id get rid of the old valve to me it dosent look like a gate but a globe . As far as needing the customer valve I think its required to install a shut off on the building main youve got a good shut off right there at the ball but Id add another close to the meter . sort of a win win to have that . could you save a buck who is going to give a damn probebly no one except the guy that changes out the meter , or mops up after him might cuz a bit.
 

Potatoes

New Member
Messages
17
Reaction score
2
Points
3
Location
Lombard, IL
I got it done today. I removed the old valve and put in a new valve on the horizontal section just after the first 90 degree turn after the water meter. Thanks again!
 

Attachments

  • IMG_6175.jpeg
    IMG_6175.jpeg
    112.5 KB · Views: 125
Last edited:
Top
Hey, wait a minute.

This is awkward, but...

It looks like you're using an ad blocker. We get it, but (1) terrylove.com can't live without ads, and (2) ad blockers can cause issues with videos and comments. If you'd like to support the site, please allow ads.

If any particular ad is your REASON for blocking ads, please let us know. We might be able to do something about it. Thanks.
I've Disabled AdBlock    No Thanks