Hi. I am having an issue with my water heater and would like some advice. Water heater is LP gas, located a few inches away from the basement wall with a vertical rise of 18 inches going straight up to the elbow with a proper pitch. All piping going out of the house meets code, doubled wall pipe, exhaust pipe above roof. I live in New York and if the weather is very cold (0-20 degrees or so) the fumes occasionally can be smelled in the basement. When this happens, the pipes are cold and have condensation, if I open the outside door to provide a draft then the pipe warms up and the fumes go up the exhaust pipe. However, now it seems that this is happening occasionally when the weather is in the lower 30s. My house is not super tight or energy efficient so a draft issue shouldn't really be a problem. There is no blockage in the vent pipes. I have a carbon monoxide monitor and it has never gone off. I am looking for a solution to this problem.
Could it possibly have anything to do with my heater being older and maybe doesn't burn as hot as it should to warm the exhaust pipe in cold weather? Could replacing this water heater with a new one be a solution to the problem?
Thank you
Does any of the vent pipe travel up the outside of the house?
Is it vented into a masonry chimney? If yes, does the chimney also vent a furnace or boiler (or did it used to be shared by a furnace or boiler?_
What is the total vertical distance from the draft hood on the water heater to the top of the flue?
Is your house heated by ducted hot air?
Duct imbalances on the heating can result in air-handler induced depressurization of the basement, which can overcome normal stack effect pressures, and backdraft the flue. This is more likely to happen when stack is cold than when the burner has been running for awhile. But once the flue has been actively chilled below some point it creates an "anti" stack effect when there is no burner adding heat to the stack, and cold air will continue to come down the flue until the flue warms up again (from either the burner firing for some period, or more slowly from the heat of the house.)
The taller the stack and the greater fraction of it that is within insulated conditioned space, the better the stack-effect draft is. But if you have tall well-ventilated attic that the flue runs through it could get cold enough between burns that it backdrafts on it's own simply from stack effect forces until the burner heats it up again. It can be complicated to analyze fully even on-site, harder still on a web forum.
If you have ducted air heating, with a smoke pencil, stick of incense or something try testing the direction of flow at the draft hood on the water heater (when the heater's burner is off), under a variety of conditions when the air handler is running. Open & close doors to different rooms to see if it ever changes. Rooms with supply-only registers and no dedicated returns are prime suspects, since a supply-duct-only pressurizes that room, and the "great outdoors" becomes part of the return path, possibly via the water heater flue.
Venting into an oversized flue that it used to share with another burner (but no longer does), is a classic "orphaned water heater" case, which will backdraft fairly readily under a variety of conditions.
You'll only get sufficient carbon monoxide to trigger the detector if there is something off with the burner, but that doesn't mean you want to be breathing the other exhaust products.