water heater vent stack

Users who are viewing this thread

fozzy12

New Member
Messages
27
Reaction score
0
Points
0
Location
North of Detroit, MI
I'm running a standard water heater in my garage. It's a 75 gal Brad White with a 4" vent. Do I need to run double insulated vent piping? I temporarily put it in with standard 4 inch vent, through a roof flashing with a storm collar and a cap. I'm getting it inspected and rather going through having it fail, I'd rather change it sooner than later. I have ample clearance where it passes through the roof and also through the second floor flooring.
I'm in Michigan if that helps.

Thanks

Eric
 

Jimbo

Plumber
Messages
8,918
Reaction score
19
Points
0
Location
San Diego, CA
At every point, including the roof, you must have 6" clearance in all directions to any piece of wood or drywall or other combustible material.
 

fozzy12

New Member
Messages
27
Reaction score
0
Points
0
Location
North of Detroit, MI
HJ,
It wasn't a question of taking a chance with single wall, I didn't know any better. I assumed since the heater had a normal 4 inch stack on top of it, that single wall would be acceptable, leaving enough clearance around the pipe. Since I have found out differently from the inspector who was kind enough to return my phone call, I will be changing it out to double wall tomorrow. It will be inspected, I just wanted it to pass on the first inspection.

Eric
 

SewerRatz

Illinois Licensed Plumber
Messages
1,681
Reaction score
10
Points
38
Location
Chicago, IL
Website
www.a-archer.net
HJ,
It wasn't a question of taking a chance with single wall, I didn't know any better. I assumed since the heater had a normal 4 inch stack on top of it, that single wall would be acceptable, leaving enough clearance around the pipe. Since I have found out differently from the inspector who was kind enough to return my phone call, I will be changing it out to double wall tomorrow. It will be inspected, I just wanted it to pass on the first inspection.

Eric

It is awsome that you are having this inspected. I was just wondering did you install this heater on an 18" stand?
 

hj

Master Plumber
Messages
33,608
Reaction score
1,049
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
heater

It only needs to be on a stand if it is in the garage. If the city has accepted the latest National Gas Code, and the heater has an FVIR burner, it only has to be on the stand if a car could impact it.
 

fozzy12

New Member
Messages
27
Reaction score
0
Points
0
Location
North of Detroit, MI
HJ
The water heater is in a separate building but since it has garage doors on it, it needs to be on a pedestal. Here it also needs to be protected from impact. That means either 4 inch steel posts filled with concrete, or a wall. I chose the wall, I planned on it anyway. It is an older heater so it doesn't have the newer burner that can sit on the floor.

Eric
 