Water Heater Vent Freezing up...

Users who are viewing this thread

SpudMuffin

New Member
Messages
18
Reaction score
0
Points
1
Location
56737
I have a tankless water heater. We had to run the vents 35' to the side of the house where there was no porch. The rise is better than 1/4" per 10'... And we used 3" PVC... However, because it has been below zero the PVC is freezing up on the inside of the pipe... Last night we had no hot water so I took a gallon of hot water and slowly poured it down the exhaust vent and that did the trick...

I figure as long as its -30 I might have to do that every other day? Any other ideas?
 
Last edited by a moderator:

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,771
Reaction score
1,191
Points
113
Location
New England
It that entire run through unheated space? Is the effective distance (this includes the additions for elbows, etc) within specs for the device? How is it terminated outside? Could it be from snow being blown in, and melting, then refreezing? Is it exiting on the side of the house with the prevailing wind?

When my boiler was installed, they installed the termination upside down...the condensate dripped down and sealed off the inlet when we had our first really cold weather. The installation manual showed it correctly, but the installers either couldn't read, or didn't look, or didn't care until they had to redo it!

index.php
 
Last edited by a moderator:

SpudMuffin

New Member
Messages
18
Reaction score
0
Points
1
Location
56737
Everything is to specs and it is installed with good slope. The run is in a crawlspace that is about 45 degrees...
 

LLigetfa

DIYer, not in the trades
Messages
7,497
Reaction score
575
Points
113
Location
NW Ontario, Canada
The rise is better than 1/4" per 10'
How much better? When I had my new furnace installed, they put such a minimum slope on it that the velocity of the exhaust kept pushing the condensate up hill. When the condensate accumulated, it got heavy and sagged the pipe so it no longer had a proper slope to drain. A few more cycles and it made gurgling noises and failed.
 

SpudMuffin

New Member
Messages
18
Reaction score
0
Points
1
Location
56737
Well I used the larger option of pipe (3") so that isn't a problem. I directed one of my heater ducts into the crawl space and that took care of it until we get back above zero...
 

Terry

The Plumbing Wizard
Staff member
Messages
29,946
Reaction score
3,460
Points
113
Location
Bothell, Washington
Website
terrylove.com
tankless-frozen-vent.jpg


-6 degrees somewhere. Not where I'm at though. I did ski in 10 degrees this week though.

This vent is on a second story roof.

tankless-frozen-vent-2.jpg
 
Last edited:

LLigetfa

DIYer, not in the trades
Messages
7,497
Reaction score
575
Points
113
Location
NW Ontario, Canada
I drive a truck for a company that delivers water to portable washcars. The washcars have atmospheric tanks that they pump from. Sometimes the tank vent builds up with ice until it is completely sealed. We get calls complaining that they are out of water but when we get there, it is just that the pump cannot suck because the vent is blocked. We have a delivery schedule so they should not run out of water unless something goes wrong. Sometimes when I get on site, I find long icicles hanging under the washcar from a water leak. Sometimes the power goes out and the inside of the washcar is a skating rink.

I had hooked up to one tank and started to fill it when I noticed the vent was blocked with ice. My truck has a boiler on board for hot water pressure jetting so I started putting hot water to the vent. Meanwhile the fill pipe was building up pressure in the atmospheric tank. When the hot water let the ice loose it shot out like a rocket.
 

Dana

In the trades
Messages
7,889
Reaction score
509
Points
113
Location
01609
A heat tape used for freeze protecting potable plumbing applied to the section of pipe that is outside of the insulation boundary of the house should work.

If the crawlspace walls aren't (yet) insulated, in a location as cool as yours (IECC climate zone 7) insulating them to the current IRC code minimum R15 continuous insulation would be worthwhile, even if there is some insulation in between the joists under the subfloor. That would mitigate against the vent condensing/ frost-up problem, but would also have a measurable heating season fuel use benefit (unless you're already at R50 between the first floor subfloor & crawlspace.)
 