Dear Fellow members,

I have a washing machine situated in a basement sitting about 6 feet below grade and the sanitary line in that areas is
running around 1.5 ft beneath grade level. The washing machine drains into a short standpipe and into the drain.
Parallel to it is a vent pipe which starts getting a lot of bubbles when the washing machine is running, Please see
attached photos for context. Please note that space is very tight in this area because the drain is so close to the
sub-floor.

Any ideas on how I can fix this setup to abate this problem would be much appreciated.

Regards.
 

Attachments

  • IMG_5586 Large.jpeg
    IMG_5586 Large.jpeg
    85.5 KB · Views: 167
  • IMG_2410 Large.jpeg
    IMG_2410 Large.jpeg
    84.5 KB · Views: 176

Terry

The Plumbing Wizard
Staff member
Messages
29,942
Reaction score
3,458
Points
113
Location
Bothell, Washington
Website
terrylove.com
Normally a washer rough looks like this.

washer_rough_1.jpg


Code requires the p-trap to be on the same floor as the washer.
 
Last edited:

Reach4

Well-Known Member
Messages
38,796
Reaction score
4,412
Points
113
Location
IL
I think the standpipe you are referring to is the thing with the nylon ties on it. The suds in the photo does not seem to have come from the top of that standpipe. Unless the suds came out explosively and the suds at the top of the stand pipe had already dripped away before the photo was taken.

The Amana 40008101 or Whirlpool 40008101 is intended to suppress suds backup from a 1-1/2 laundry standpipe. I don't know if that would help your situation.
 

wwhitney

In the Trades
Messages
6,532
Reaction score
1,822
Points
113
Location
Berkeley, CA
Your vent should not be open to the atmosphere, that will let sewer gasses (and suds!) out. So you need to run that vent up through the subfloor and connect it to a vent that goes through the roof.

Cheers, Wayne
 

Reach4

Well-Known Member
Messages
38,796
Reaction score
4,412
Points
113
Location
IL
Ahh.., that is an open vent. I was wondering what was going on there. I would top that with an AAV. Your standpipe is not to code anyway, so I don't think worrying about whether an AAV is up to code for you matters.
 

Cdibuff

New Member
Messages
21
Reaction score
0
Points
1
Location
Palo Alto
Ahh.., that is an open vent. I was wondering what was going on there. I would top that with an AAV. Your standpipe is not to code anyway, so I don't think worrying about whether an AAV is up to code for you matters.
Will the AAV on top of the vent prevent the bubbles from forming? The setup is pretty tight and it is impossible to get the vent to go up higher than it is, unless it is routed out horizontally.

I understand none of these solutions are ideal or code compliant but this is the best we can do in this space. We have had the sump pump arrangement but that just keeps having leaks. I am out of ideas.
 

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,770
Reaction score
1,190
Points
113
Location
New England
The suds will keep forming, but the AAV only lets air in, and is normally closed under pressure. The soap suds may build up and the gunk may eventually cause the thing to fail.

Depending on how the other things on that drain line are configured, just capping that pipe might work just as well. What you're looking for is that the WM trap doesn't get sucked dry by other things draining into that line. If the trap stays full enough, it will work without letting sewer gasses into the home. That should be easy to test...some plastic and a big rubber band or tape and you can cap that off.
 

Reach4

Well-Known Member
Messages
38,796
Reaction score
4,412
Points
113
Location
IL
Will the AAV on top of the vent prevent the bubbles from forming? The setup is pretty tight and it is impossible to get the vent to go up higher than it is, unless it is routed out horizontally.
The AAV will prevent foam coming out.

You will need to make the vertical that the AAV fitting glues to leave enough space for the AAV. So I think you will cut the current 45, extend a bit past the joist, and then 45 up.

The AAV vent bottom will not need to be as high as the current opening. Cut the new vertical be least 4 inches higher than the trap arm ( output of the trap). Then glue on the fitting that the AAV will screw into.

AAV itself cannot be at a 45 degree angle. It must be installed on a vertical pipe that is within 15 degrees of plumb.
You will need to be able to change out the AAV, so have enough space below the ceiling/subfloor.
 
Last edited:

Cdibuff

New Member
Messages
21
Reaction score
0
Points
1
Location
Palo Alto
I think the standpipe you are referring to is the thing with the nylon ties on it. The suds in the photo does not seem to have come from the top of that standpipe. Unless the suds came out explosively and the suds at the top of the stand pipe had already dripped away before the photo was taken.

The Amana 40008101 or Whirlpool 40008101 is intended to suppress suds backup from a 1-1/2 laundry standpipe. I don't know if that would help your situation.
You are correct. The suds do not come out of the standpipe (where the washer drain pipe is inserted), They come out of the open vent pipe adjacent to it.
 

Cdibuff

New Member
Messages
21
Reaction score
0
Points
1
Location
Palo Alto
The suds will keep forming, but the AAV only lets air in, and is normally closed under pressure. The soap suds may build up and the gunk may eventually cause the thing to fail.

Depending on how the other things on that drain line are configured, just capping that pipe might work just as well. What you're looking for is that the WM trap doesn't get sucked dry by other things draining into that line. If the trap stays full enough, it will work without letting sewer gasses into the home. That should be easy to test...some plastic and a big rubber band or tape and you can cap that off.
I like your idea. Is a vent really required for a washer? I have only seen standpipes with a p-trap. So, it appears that I should be able to cap the vent. Just hoping that with a short standpipe the water from the washer will not spill out of that standpipe.

The whole issue is that the the drain is a few feet above the washer and there is no way to have a longer standpipe.
 

wwhitney

In the Trades
Messages
6,532
Reaction score
1,822
Points
113
Location
Berkeley, CA
The whole issue is that the the drain is a few feet above the washer and there is no way to have a longer standpipe.
But the suds are coming out of the vent.

So if you can get the vent under a wall above with an existing vent, you can extend the vent up into that wall, and connect to the existing vent at least 6" above the upper fixture flood rim. You can move the vent by some combination of moving the washing machine; moving the standpipe relative to the washing machine; and moving the vent takeoff relative to the standpipe. The vent takeoff just has to be within 60" horizontally and 2" vertically of the p-trap outlet.

That's the correct solution to your problem.

Cheers, Wayne
 

Cdibuff

New Member
Messages
21
Reaction score
0
Points
1
Location
Palo Alto
But the suds are coming out of the vent.

So if you can get the vent under a wall above with an existing vent, you can extend the vent up into that wall, and connect to the existing vent at least 6" above the upper fixture flood rim. You can move the vent by some combination of moving the washing machine; moving the standpipe relative to the washing machine; and moving the vent takeoff relative to the standpipe. The vent takeoff just has to be within 60" horizontally and 2" vertically of the p-trap outlet.

That's the correct solution to your problem.

Cheers, Wayne
There is no space in that area to vent out vertically through the building. My question though is, is a vent really necessary? The standpipe that the washer drains into has a p-trap. The washer drain is obviously loose inside the 2" standpipe (so there should not be any vacuum formation). Can I just cap off that vent and the problem gets solved, as

suggested by jadnashua earlier in this thread?​

 

wwhitney

In the Trades
Messages
6,532
Reaction score
1,822
Points
113
Location
Berkeley, CA
Depending on how the other things on that drain line are configured, just capping that pipe might work just as well. What you're looking for is that the WM trap doesn't get sucked dry by other things draining into that line. If the trap stays full enough, it will work without letting sewer gasses into the home. That should be easy to test...some plastic and a big rubber band or tape and you can cap that off.
While it may work at the moment, that's a bad solution, as you are setting it up to siphon in the future under different conditions (backup, change in fixtures, etc). So that shouldn't really be suggested as viable solution.

Putting an AAV on is a possible compromise, with the understanding that because of the sudsing, the AAV should be checked periodically for proper function, more so that typical.

Cheers, Wayne
 

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,770
Reaction score
1,190
Points
113
Location
New England
A proper vent prevents siphoning of the p-trap. But, what is flowing down the drain will determine if that can happen, so with the right set of conditions, yes it would be siphoned. Since your pseudo vent is open and not being blocked by a p-trap, you have an opening in the house to the sewer, so the trap is essentially useless.

Suds will gunk up the AAV. How long that takes, can't say. While it's functioning, it should help.
 