Basic layout is fine. A few comments:
- UPC requires the sink vent takeoff to be a combo, not a san-tee on its back.
- The kitchen sink trap is typically outside the wall.
- The 4" minimum trap arm length is measured between the trap weir (the point where the bottom of the trap outlet starts to slope downward) to the near interior face of the vertical yellow vent. In practice, 2" of exposed plastic pipe between hubs is well over 4".
Cheers, Wayne