Some codes would not permit that. However IPC, which you are under, is fine with that. It seems unlikely that Florida would have modified that aspect of the IPC code.My question is about the green connector in the following image. I have recently learned that a sanitary tee is never supposed to be in this "on it's back" position. However, this is for a vent with no waste flow. Should I change this to a sanitary wye?
IPC says that a laundry standpipe plus anything else must feed into 3 inch pipe or bigger. Whether there is a an amendment not requiring you to use 3 inch, or if the inspector is applying a looser pragmatic interpretation, you look like you are OK. But I am pretty sure that the IPC itself does not have an easier specification for residences. So smile, and say thanks. Two inch is going to do fine.
While in that wall, you could consider adding a cleanout above the bottom santee. If you did get a blockage, it would probably be under the slab as flow turns from vertical to horizontal. That curve should be a long sweep, but chances are it is not. A medium bend may have been allowed when that concrete was poured.
From the cleanout down you would want 2 inch.