vents and windows

Users who are viewing this thread

Barrybpdx

New Member
Messages
41
Reaction score
0
Points
0
Location
portland, or
i'm doing a big remodel, finishing the 3rd floor attic as living space w/ a dormer bathroom. also moving fixtures in a 1/2 bath in a 1-story section (former porch) off the back of the house.

what is the requirement about how far a roof vent needs to be from an operable window?
something like the end of the pipe must be 2' above any window within 10' horizonally?
 

Winslow

Plumber
Messages
445
Reaction score
0
Points
0
Location
Hawaii
according to the UPC you need to be 10 away horizontally or three feet above any openable window or air intake
 