Using a Sanitary Tee as Vent directly connected to P-Trap trap?

Users who are viewing this thread

CrackedCastIron

New Member
Messages
5
Reaction score
0
Points
1
Location
Washington State
First pic shows what I believe would be a standard install. P-Trap + P-Trap elbow, connected to a vent.

Second pic shows using a sanitary tee RATHER than the elbow that came with the P-Trap, functioning as both the P-Trap elbow and as the vent coming out the top.

Are there any issues with this plan?

I'm doing a retrofit of a washer/dryer hookup. Small 24" front-load washer/dryer. Due to the location I only have a single stud bay to work with, so I'm trying to be as horizontally tight as possible. I save a ton of space with the second pic but want to be sure I won't hit any issues due to the deep trap or direct vent.



zGv4CKSl.jpg


QGDYLAsl.jpg
 
Last edited:

CrackedCastIron

New Member
Messages
5
Reaction score
0
Points
1
Location
Washington State
Did some more research and found the term, the second picture is a non-code "Crown Vent" Looks like I'll find another way.

I'd still be interested in hearing why that is not code, if anyone known. From my perspective the crown vent would prevent a syphon of the trap.
 

CrackedCastIron

New Member
Messages
5
Reaction score
0
Points
1
Location
Washington State
Not to scale unfortunately. I'm far more than 5' to the stack.

This single stud bay is really my only option for venting. The rest of the pipe's length it's running under an electrical conduit with no room to pass upwards as a vent inside the stud wall.

I can either vent it entirely with fixtures in the single stud bay.

Or, I can run a vent in the stud bay directly to the left of this one. I only have 2-3' before I hit the circuit breaker. So the vent would have to turn, go through the stud, and then go up in the original stud bay.

Maybe that is the best option, but it's also my understanding that a vent cannot go horizontal while it's still below the fixture's flood plain..?
 

Reach4

Well-Known Member
Messages
38,796
Reaction score
4,412
Points
113
Location
IL
img_4.jpg
Don't have the p-trap in the same vertical plane as the vent and drain lines. Rotate the trap so that it fits between studs or other instructions. If the standpipe extends into the room rather than fitting a recessed box, it might be partially hidden behind the washer anyway.

Note that I turned your venting fitting around in the picture.
 

Attachments

  • img_2.jpg
    img_2.jpg
    101.4 KB · Views: 548
Last edited:

MACODEDOC

New Member
Messages
24
Reaction score
0
Points
1
Location
Massachusetts
In Mass using TY on it's back is Legal for a vent only, I would change your direction of flow of the TY to drain condensate and help with air flow
 