bengal21
New Member
Hello,
If someone could answer the following question for me it would be appreciated. And the units I am using are from the UPC.
If I have a 2" vent that can serve a total of 24 FU can I split the fixtures on opposite sides of the room into 1.5" vents (as long as each side doesn't exceed 8 FU) and tie them together into a 1.5" x 1.5" x 2" tee to run up to connect with the main stack? They would all run vertical until 6" above the flood elevation of the highest fixture.
Am I correct in summing the FU for each vent branch? i.e.
Vent one (1.5") has a total of 7 FU and Vent two (1.5") has a total of 5 FU so each vent alone is under the 8 FU for a 1.5" vent. So tying them together for a total of 12 FU in a 2" vent is acceptable because it is under 24 FU?
Thanks for all of the expert advise received. It is tremendously helpful.
If someone could answer the following question for me it would be appreciated. And the units I am using are from the UPC.
If I have a 2" vent that can serve a total of 24 FU can I split the fixtures on opposite sides of the room into 1.5" vents (as long as each side doesn't exceed 8 FU) and tie them together into a 1.5" x 1.5" x 2" tee to run up to connect with the main stack? They would all run vertical until 6" above the flood elevation of the highest fixture.