Tub/Shower Combo to Shower Only Conversion - Post Tension Slab

Users who are viewing this thread

Dogwell

Member
Messages
47
Reaction score
0
Points
6
Location
Arizona
Hi All. We have a new build house and are doing some tub to shower conversions. The house is in AZ on post tension slab. I had a plumber come out today to give me a quote and I didn't quite understand why he was saying we'd need to cut into the slab. I've always been advised with post tension, you absolutely do not want to to cut the concrete. Here are some photos showing what we are working with.

Can someone please explain to me the best way to deal with this 1.5" drain to 2" conversion? I was under the impression that the pipe could be cut where I have marked a red line and a long sweep 90" could be introduced. What am I missing? Why would we need to cut into the slab?

Many thanks!

We are hoping to use either KBRS shower basin or Schluter shower pan if that makes a difference. Thank you.
 

Attachments

  • Screenshot_20220422-211902_Gallery.jpg
    Screenshot_20220422-211902_Gallery.jpg
    71.8 KB · Views: 146
  • Screenshot_20220422-211845_Gallery.jpg
    Screenshot_20220422-211845_Gallery.jpg
    65.5 KB · Views: 161
  • Screenshot_20220422-211830_Gallery.jpg
    Screenshot_20220422-211830_Gallery.jpg
    61 KB · Views: 137
  • Screenshot_20220422-211810_Gallery.jpg
    Screenshot_20220422-211810_Gallery.jpg
    81.5 KB · Views: 178
  • Screenshot_20220422-211801_Gallery.jpg
    Screenshot_20220422-211801_Gallery.jpg
    97 KB · Views: 141
  • Screenshot_20220422-211748_Gallery.jpg
    Screenshot_20220422-211748_Gallery.jpg
    86.2 KB · Views: 140

Breplum

Licensed plumbing contractor
Messages
1,904
Reaction score
767
Points
113
Location
San Francisco Bay Area
Showers universally use and are required to be 2". That includes the p trap and drain line.
Have I seen dirtbag situations where someone tried to get away with smaller, yes. Did it work? sort of...not well.
 

wwhitney

In the Trades
Messages
6,532
Reaction score
1,822
Points
113
Location
Berkeley, CA
2" for the shower is the UPC requirement, but the IPC does allow 1-1/2" for less than 5.7 gpm of showerheads.

What the dimensions of the new shower going to be, and what sort of drain? If the drain is going to be basically over the existing tub waste and overflow, then I expect you could make things work with the existing trap and without cutting concrete. Otherwise, you'll need to move the trap and cut into the concrete.

Cheers, Wayne
 