I've attached a photo of my expansion tank and the piping at the top of my water heater. I'm feeling confident about my expansion tank having failed. The tank is really heavy like its full of water. I depressed the Shrader valve and nothing came out. Not water or air.
Yes, the water pressure at a hose bib outside of the house is a constant 60-65 PSI, even when the pressure at the drain bib on the water heater reaches 140 PSI after heating the water back up after a shower or bath. That tells me the problem is not the City regulated water supply, but is the water heater set-up, right? Do I have what is considered a closed system because of the one-way check valve on the water inlet?
This was mentioned above by Terry:
"Has anyone taken the pressure at the water heater, with the heat turned off?
It may be that the front bib has a reducer on it for irrigation purposes.
In all my years of plumbing, I've never had cold water to a water heater, heated up to 125 degrees ever get over 90 PSI"
The water heater pressure hasn't been recently checked with the burner off, but the problem stopped for a few weeks and the pressure read no more than 80 PSI at the water heater drain bib and the tp valve stopped releasing water. That seemed OK to me. I was confused as to why the problem stopped/started up again. I don't think the bib on the water heater drain has a reducer for this reason.