Toilet with only upstream dry vent. Now what?

Users who are viewing this thread

Radio Flyer

Member
Messages
38
Reaction score
6
Points
8
Location
Rutland, VT
Filed under "stuff in my house then doesn't seem right" is this toilet DWV setup. The toilet flange connects to the wye you see, and the line is vented just upstream.

PXL_20220327_200730507~2.jpg


PXL_20220327_200904072~2.jpg


Again, the only venting on this line is upstream from all fixtures, including the toilet. You can just barely see the vent going up on the left side of the photo.

Previously a washing machine also drained into the line just downstream where the temporary black cap is now (see photo).

PXL_20220327_200812461~2.jpg


The washer standpipe was vented above, so maybe the idea was that it served as a wet vent for the toilet? But that still leaves a horizontal section of unwashed vent pipe upstream from the toilet. I don't know why it is there. (And a door now swings through the area where the standpipe was previously located.)

I suppose I could remove the toilet to install a closet bend, reroute the line to get underneath the outside wall, and then go up with a combo for the vent (at no less than 45° down from the vertical, right?). That would eliminate the upstream vent, though it would require removing the ceiling above to connect the new vent, since there is no access currently.

I guess my question is, do I need to move heaven & earth to change this, or should I just cross my fingers? (I suppose if I ever get a blockage on this line I could rinse the vent from the roof??) Thanks for any help.
 

Attachments

  • PXL_20220327_200904072~2.jpg
    PXL_20220327_200904072~2.jpg
    44.5 KB · Views: 82

wwhitney

In the Trades
Messages
6,559
Reaction score
1,842
Points
113
Location
Berkeley, CA
No opinion on the magnitude of the problem and whether it requires fixing it.

To fix it, you could see if the following arrangement would fit in the available height. Left-right is parallel to the joists in the first picture:

Closet flange - closet bend with outlet pointing left - 3" san-tee with the barrel at a 45 degree angle, pointing up and towards the vent - 45 on the top of the san-tee to connect to the existing 3" vent - LT90 on the bottom of the san-tee to turn horizontal to the right and connect to the existing 3" drain below the joists.

Cheers, Wayne
 

Radio Flyer

Member
Messages
38
Reaction score
6
Points
8
Location
Rutland, VT
I would leave it alone. If you ever do get a clog at that 90 degree turn you can snake and wash it out from the roof.
I think I can manage that! Thank you.

Wayne's idea is also helpful, though since I'm up against a rim joist in the corner of the house, it would be difficult.

Again, thank you for the help!
 