Toilet Vertical Drain Rough-in

Users who are viewing this thread

theHaas

New Member
Messages
2
Reaction score
0
Points
1
Location
houston
Every diagram I've found has the toilet flange draining to a closet bend before connecting to a soil stack.

I'm roughing in a 3" drain for a toilet on the 2nd floor house new construction. The Flange perfectly lines up with a 1st floor interior stud wall. Can I use a sanitary 3" 3" 2" T and drain vertically 12' to street 90 in the crawl space and then vent from same said T thru attic?

I pray you well and appreciate the assist

ryan
 

wwhitney

In the Trades
Messages
6,532
Reaction score
1,822
Points
113
Location
Berkeley, CA
You can use a 3x3x2 wye with the 2" as your dry vent. A dry vent needs to come off on the vertical and stay vertical until 6" above the floor rim level. Here "vertical" includes up to 45 degrees off plumb.

Cheers, Wayne
 

theHaas

New Member
Messages
2
Reaction score
0
Points
1
Location
houston
You can use a 3x3x2 wye with the 2" as your dry vent. A dry vent needs to come off on the vertical and stay vertical until 6" above the floor rim level. Here "vertical" includes up to 45 degrees off plumb.

Cheers, Wayne

You can use a 3x3x2 wye with the 2" as your dry vent. A dry vent needs to come off on the vertical and stay vertical until 6" above the floor rim level. Here "vertical" includes up to 45 degrees off plumb.

Cheers, Wayne


thank you Wayne...
 