Toilet DWV fittings?

Users who are viewing this thread

Adam00

New Member
Messages
8
Reaction score
0
Points
1
Location
VA
2015 IPC

Toilet flange goes to 4" PVC.
If I drop down to a long 90* into a sanitary T there is a good chance people will hit their head.
If I use a 45* and a 45* Y no one would ever hit their head.
I can only go so high due another fitting.
The sanitary T or the 45* would go into the main 4" stack that goes out the roof.

Witch way is better and to code?
 

Terry

The Plumbing Wizard
Staff member
Messages
29,942
Reaction score
3,459
Points
113
Location
Bothell, Washington
Website
terrylove.com
If the toilet is going into a vertical santee, then a medium 90 from the flange to the santee works.

dwv_b2.jpg


If you are dropping down to a horizontal line, then the fitting is a wye where it meets the 4".
 