I'm not sure how to make this repair properly (and without tearing the side of my house apart). I could use some tips or suggestions.
Original construction had an exterior light fixture mounted to a wood block sized 7.25" W x 9"H x 1.5", mounted over lap siding per the picture. (The wood block also had routered edges cut at a 45 degree angle.) A hole in the center of the block (maybe 2" wide) provided access between the ROMEX supply wires and fixture's wires, and held the wire nuts. The round light fixture box was left open, supplying the ROMEX wires. The block weathered and split, the screws holding the fixture mounting plate popped out, and the fixture came loose. I disconnected the fixture at the wire nuts, pulled it down, and tore out the wood block. Time for the fix.
The first problem is that the wire nuts were not inside a proper electrical enclosure, but inside the (combustible!) wood block. The second problem is that the electrical mounting box is off-center from where it should have been. It's crowding the window trim, making use of a standard commercial mounting block a difficult or impossible. The third problem, was inadequate flashing, and the now missing house wrap.
#3 is easy enough to resolve, if not "to manufacture specs", but water proof enough. I'll use flashing tape at the edges over the house wrap under the siding edge, and over the OSB sheathing, with a metal drip cap over the top of the block.
Resolving #2 "properly" would probably require moving the round electrical box to center. That would likely require removing the lap siding, cutting into the sheathing, and then fixing the damage done to the sheathing and siding. Then I could use a commercially available plastic mounting block designed for the purpose.
Alternative, custom solution for #2 (and also #1): I'd prefer to install a round plate cover over the existing box, leave the wire nuts inside that box, and run the fixture wiring through the plate cover. (Problem #1: What kind of watertight connector can be used for the fixture wires entering that plate cover?) And, of course, I'd cut out a new wood mounting block the same size as the original.
I'd have to cut a large enough hole through the replacement block to both (a) enable the fixture to center mount, with the wires passing through rear though the block, and (b) to expose the center of the plate cover and watertight connector, so that the fixture wires can enter the box through the box cover. (The cover would remain partially blocked, but visible under the light fixture.)
Problem #2: My understanding is that per code, all plate covers need to be exposed and accessible. With my alternate solution, the round plate cover would be hidden behind the block and the light fixture. However, I also understand that the exterior light fixture itself is considered an electrical box, i.e. the wire nuts could be behind that, if it wasn't sitting over a combustible wooden block.
I think my solution will work well enough, even if it's ... "inelegant".
Ideas? Recommendations? Sarcasm?
Thanks.
Original construction had an exterior light fixture mounted to a wood block sized 7.25" W x 9"H x 1.5", mounted over lap siding per the picture. (The wood block also had routered edges cut at a 45 degree angle.) A hole in the center of the block (maybe 2" wide) provided access between the ROMEX supply wires and fixture's wires, and held the wire nuts. The round light fixture box was left open, supplying the ROMEX wires. The block weathered and split, the screws holding the fixture mounting plate popped out, and the fixture came loose. I disconnected the fixture at the wire nuts, pulled it down, and tore out the wood block. Time for the fix.
The first problem is that the wire nuts were not inside a proper electrical enclosure, but inside the (combustible!) wood block. The second problem is that the electrical mounting box is off-center from where it should have been. It's crowding the window trim, making use of a standard commercial mounting block a difficult or impossible. The third problem, was inadequate flashing, and the now missing house wrap.
#3 is easy enough to resolve, if not "to manufacture specs", but water proof enough. I'll use flashing tape at the edges over the house wrap under the siding edge, and over the OSB sheathing, with a metal drip cap over the top of the block.
Resolving #2 "properly" would probably require moving the round electrical box to center. That would likely require removing the lap siding, cutting into the sheathing, and then fixing the damage done to the sheathing and siding. Then I could use a commercially available plastic mounting block designed for the purpose.
Alternative, custom solution for #2 (and also #1): I'd prefer to install a round plate cover over the existing box, leave the wire nuts inside that box, and run the fixture wiring through the plate cover. (Problem #1: What kind of watertight connector can be used for the fixture wires entering that plate cover?) And, of course, I'd cut out a new wood mounting block the same size as the original.
I'd have to cut a large enough hole through the replacement block to both (a) enable the fixture to center mount, with the wires passing through rear though the block, and (b) to expose the center of the plate cover and watertight connector, so that the fixture wires can enter the box through the box cover. (The cover would remain partially blocked, but visible under the light fixture.)
Problem #2: My understanding is that per code, all plate covers need to be exposed and accessible. With my alternate solution, the round plate cover would be hidden behind the block and the light fixture. However, I also understand that the exterior light fixture itself is considered an electrical box, i.e. the wire nuts could be behind that, if it wasn't sitting over a combustible wooden block.
I think my solution will work well enough, even if it's ... "inelegant".
Ideas? Recommendations? Sarcasm?
Thanks.