I am going to buy a tekmar 256 outdoor reset control. I have a question on wiring from the 7 terminal on the tekmar 256 to the R wire on thermostat. I have 4 zones wired to a sr504 taco switching relay. Should I wire all 4 red wires to the 7 terminal?
 

Fitter30

Well-Known Member
Messages
4,292
Reaction score
778
Points
113
Location
Peace valley missouri
Don't touch taco control wiring. Taco control can be wired two ways just heating and heating with dhw priority. Heating only #5 termials in series with a T wire from taco control. 7 to 9 can eithe r be jumped or add a 5 amp 24vac relay spst n.o. relay w to c from thermostat, contacts wired across tekmar 7 to 9. If system is using dhw take picture of boiler wiring diagram.
 

Paul Jones

New Member
Messages
2
Reaction score
0
Points
1
Location
New Hampshire
Don't touch taco control wiring. Taco control can be wired two ways just heating and heating with dhw priority. Heating only #5 termials in series with a T wire from taco control. 7 to 9 can eithe r be jumped or add a 5 amp 24vac relay spst n.o. relay w to c from thermostat, I wired across tekmar 7 to 9. If system is using dhw take picture of boiler wiring diagram.
Thanks. I connected the xx on taco relay to 7 and 9 on tekmar, connected 5 and 6 on tekmar to unused tt terminals on aquastat to 5 and 6 on tekmar, seems to be working fine.
 